The manufacturers can tell you the maximum flow that should be allowed
through one of their appliances.  Many - but not all - put that
information on their loss curves, sometimes shown as an open circle or
diamond on the curve itself.    These are RATED flows, but not the
absolute maximum that can be run through the appliance; the curves
themselves usually extend well beyond that point, so the devices have
been tested and certified at higher flows than the rated maximum.
I'll leave it to somebody smarter than me to explain how all that works
...

Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd
Williams
Sent: Friday, April 15, 2011 10:42 AM
To: [email protected]
Subject: BFP maximum flows

When sizing a backflow preventer for a job, what flow should be
considered the maximum for the device? Is the Rated Flow the maximum?
Can it be taken out to a UL Tested flow (which some manufacturer's
include in their graph)? I tried to look  it up but didn't find
anything.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to