Ok, got it to work with the sprinks and the remote 1.5" interior hose reel 
flowing simultaneously.  By bumping the required pressure for the hose reel it 
increased pressure within the entire system causing the sprinklers to flow far 
more than required.  Dropped the sprinks from 8K to 5.6K, still met the flow 
req's for the sprinks and if I need to prove I can flow one interior hose, I 
can.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Thursday, April 21, 2011 4:25 PM
To: [email protected]
Subject: RE: Combination standpipe riser & hose flows

That sounds okay to me.  If you can make the Class I's work, then the Class 
II's should as well, eh?

SML



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, April 21, 2011 1:09 PM
To: [email protected]
Subject: RE: Combination standpipe riser & hose flows

Not considered a high rise.  Supply is automatic.

I've calc'd the standpipe alone and can make it work from the automatic source 
(fire pumps from 1MM gallon on-site storage water tank)

I can make the sprinklers by themselves work from the same source.

It's just if they are put together that it won't work.  Not enough pressure.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Thursday, April 21, 2011 4:03 PM
To: [email protected]; [email protected]
Subject: RE: Combination standpipe riser & hose flows

Is the building considered a high-rise?   Is the Class I standpipe system an 
automatic or manual water supply?    

The collective intent of 13 and 14 is that you have to hydraulically prove the 
most demanding condition(s) of the sprinkler and standpipe systems 
individually, but not concurrently.   So if you're hydraulically calculating 
the Class I standpipe component you need to know if you're calculating from the 
automatic source or the FDC (manual system).   To add Class II components, you 
will have to do an automatic calculation in accordance with 14.   For the 
sprinklers, you would design hydraulically per 13.    Contrary to popular 
practice, you don't have to take an inside hose when you have a sprinkler 
system, only when you have hose valves supplied by a sprinkler system that are 
not considered a standpipe system.

The foregoing is my opinion only and does not necessarily represent the opinion 
or intent of the NFPA 14 Technical Committee on Standpipe and Hose Systems.

Steve Leyton
Protection Design & Consulting
San Diego, CA

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, April 21, 2011 12:56 PM
To: [email protected]; [email protected]
Subject: Combination standpipe riser & hose flows

Admittedly I'm kind of at an impasse.  

I've got a 4 level open process structure.  Top level is about 85ft above 
grade.  Non-occupied.  The structure is provided with a dry sprinkler system 
and has 2.5" hose outlets at intermediate landings.  The owner has requested 
1.5" hose reels at each floor for their responders.  

The area of the upper floor is only about 1400 sq. ft.  Due to obstructions and 
some equipment that requires impingment protection the number of heads flowing 
is about 33.

The structure is fully sprinklered.

When calculating the sprinkler flow I'm trying to decipher the text in NFPA 13 
and 14 (2010) concerning how to include or not, the flow and pressure required 
for the 2.5" hose connections.

If I flow 500 gpm through the top two 2.5" valves I'm good.

If I have to provide for 250 gpm in addition to the sprinkler flow I'm good.

Where I'm in the toilet is if I have to provide that 2.5" valve at 250 gpm AND 
at 100 psi.  

13 makes it sound like I don't have to include the hose flow if my sprinkler 
flow is the higher value NFPA 13-2010 12.8.5(2) but this is referring to wet 
system, no reference to dry systems.  

But if that is true, and I don't have to include the extra hose flow, do I 
still need to provide 100 psi at that outlet?  

Am I missing something here?

Is it assumed there will be simultaneous flow of the 2.5" hose AND sprinklers?


Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to