NFPA #13 (2007)
8.7.3.1.4  Sidewall spray sprinklers shall not be installed back-to-back
without being separated by a continuous lintel or soffit.



On Mon, Apr 25, 2011 at 7:35 AM, Eric Tysinger <er...@waynefire.com> wrote:

> Well NFPA 13 doesn't address sidewalls installed back to back (that I could
> quickly find). Is there a beam that runs down the peak that you would be
> hanging the line under? If so you would have to come out each side then up
> into the pocket area anyway. So the beam would be located between the
> sidewalls.
>
>
> Thanks,
> Eric Tysinger CET
> NICET III - 108988
> Designer
> Wayne Automatic Fire Sprinklers, Inc.
> 4370 Motorsport Drive
> Concord, NC 28027
> p: (704)782-3032 x1751
> f: (704)795-6838
> C: (239)633-9703
>
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org [mailto:
> sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
> Sent: Monday, April 25, 2011 10:25 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: EC Sidewall Heads
>
> I talked with one of the engineers at Victaulic and he said installing them
> back to back would not be a problem, I asked if the wall wetting would cold
> solder the heads and he said no...... hmmm.
>
> Brian Harris
> FDFP Inc.
>
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Eric
> Tysinger
> Sent: Monday, April 25, 2011 10:20 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: EC Sidewall Heads
>
> As you know smooth and flat doesn't mean it has to be horizontal. However
> the exposed timber makes it not smooth and flat anymore. I think and I may
> be wrong, but if you were to individually protect each pocket with a
> sidewall sprinkler it may be acceptable, but where you are going to run into
> a problem is with the sidewalls placed back to back. Since sidewalls also
> throw back you would have to use a baffle of some sort between them, which
> would be near impossible anyway.
>
> I say stick to the 2 lines.
>
>
> Thanks,
> Eric Tysinger CET
> NICET III - 108988
> Designer
> Wayne Automatic Fire Sprinklers, Inc.
> 4370 Motorsport Drive
> Concord, NC 28027
> p: (704)782-3032 x1751
> f: (704)795-6838
> C: (239)633-9703
>
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian
> Harris
> Sent: Monday, April 25, 2011 10:10 AM
> To: sprinklerforum@firesprinkler.org
> Subject: EC Sidewall Heads
>
> I've done my homework and am looking for some expert confirmation. We have
> a bank that has a entry way that has exposed timber ceilings and now that
> our pipe is installed the Architect is asking if we can re-do it with a
> single line of back to back ECOH sidewall heads running down the peak in
> between each pocket. My original thought was we could probably make that
> work but after looking into it a little deeper I don't think it's an option.
> 8.4.2
> (07) says sidewall heads can only be installed under smooth flat ceilings &
> 8.4.3 (07) says extended coverage heads can only be installed under
> .unobstructed or noncombustible obstructed construction.  So at this point
> I'm leaning towards keeping the (2) branch lines with uprights, yes?
>
>
>
> Brian Harris
>
> First Defense Fire Protection
>
> 11957 Ramah Church Road
>
> Huntersville, NC 28078
>
> Phone: 704.948.3506
>
> Fax: 704.948.3507
>
> Nicet # 128476
>
>
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17320)
> http://www.pctools.com/ =======
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: supp...@firesprinkler.org
>
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: supp...@firesprinkler.org
>
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17320)
> http://www.pctools.com/ =======
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17320)
> http://www.pctools.com/ =======
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: supp...@firesprinkler.org
>
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: supp...@firesprinkler.org
>
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to