And 71.5 psi is 110 percent of the pumps rating.

Mike Bell
Senior Designer

Aero Automatic Sprinkler Company
21605 N. Central Avenue
Phoenix, AZ  85024
(623) 580-7848 Office  (623) 229-4980 Cell
(623) 580-5230 Fax
aerofire.com



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Thursday, June 02, 2011 6:37 AM
To: '[email protected]'
Subject: RE: Gravity Tanks

Is 71.5 the churn pressure of the pump? The pump will produce pressures higher 
than rated pressure when the flow is lower than rated flow.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Thursday, June 02, 2011 8:31 AM
To: [email protected]
Subject: Gravity Tanks

Reviewing some calc's for a job that has a 30,000 gallon tank (gravity) that
feeds a 500gpm @ 65psi pump that sits approx. 7' below the pump suction, no
other sources of water supply. The current calc's show a static pressure of
71.5, residual of 65, and a flow of 500. I'm having a hard time coming up
with the static of 71.5, what am I missing?

 

Brian Harris, CET

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17450)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to