I did see that. The discharge velocity at 150% is 18fps. I am curious what 
people have come across since the 20fps note is in the annex and the code 
itself does not make any explicit exception.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Morey, Mike
Sent: Tuesday, July 19, 2011 12:16 PM
To: [email protected]
Subject: RE: Pump Discharge Piping

I believe if you look in the "discharge pipe" section of 25 and the associated 
annex material you'll find the sizes are intended to keep the velocity below 
20'/sec.  There really isn't any exception, but the discharge size is only 
mandated between the fire pump discharge flange and the discharge shutoff 
valve, normally there's only a couple fittings and valves in that space, 
anything after the discharge shutoff is considered NFPA 13 governed system pipe 
and can be any size supported by calcs.
 
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.439.2695
www.bmwc.com

________________________________

From: [email protected] on behalf of Matt Grise
Sent: Tue 7/19/2011 11:56 AM
To: '[email protected]'
Subject: Pump Discharge Piping



Are there any exceptions out there for the minimum pipe sizing on fire pump 
discharge as listed in NFPA 20 2007 5.25? We have calc'd a pump and all of the 
down stream piping to work with a smaller diameter than the one listed in the 
table. Is there additional thrust blocking or supports that can be added to 
allow a smaller pipe size? I am thinking that the goal is to keep the velocity 
down to reduce water hammer effects? Is that the case - are there other 
considerations?

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to