NFPA 22, 2008 7.2.3.1 The water filling pipe shall be at least 1-1/2" in size, shall be run separately from the filling pump or other acceptable source of supply, and shall be adequately supported and protected from mechanical injury.
7.2.3.2 The filling pipe shall be connected to the top or bottom of the tank as required by the authority having jurisdiction. 7.2.3.3 A listed horizontal bronze-seat swing check valve and a renewable seat globe valve shall be provided near the tank. 7.2.3.4 The globe valve shall be placed between the check valve and the tank. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Tuesday, July 26, 2011 4:23 PM To: [email protected] Subject: tank fill line As far as I can tell, the tank fill line doesn't have to be listed for fire service. Can anybody confirm this? Thanks, Greg -- Greg McGahan Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)