I have a project were the AHJ did some field fire testing on a canopy and
decided that since a sample the thermoplastic ROOF membrane "sustained flame
after an exposure to flame", sprinklers were required in the canopy.

 

I thought the canopy meet the exceptions of 8.15.7.3 (2).  

 

I didn't think the material on top of the canopy was a consideration. This
canopy is constructed with a EIFS (FSI <25) attached to 2 layers of exterior
gypboard attached to the bottom of 2x12's(joist spaces @22ft^3) with OSB and
built up TPO roofing on top.

 

Am I wrong in thinking that we are protecting the canopy from ignition
sources underneath it, not above it?

 

Thanks for any insight or help,

 