It is not what you say it how you say it. You get in trouble when you intermingle NFPA-25 inspection with design statements. Legally when this is done you have changed the scope of the inspection resulting in really bad things. The key to making an "engineering call" is to keep it outside the inspection in a separate letter or in a clearly designated part of inspection titled observation with a clear statement such as:
INSPECTION OBSERVATION(S) ADDENDUM Items listed below are not part of an NFPA 25 Inspection and are outside of the scope of the Inspection Agreement with the Company. The identification of these items does not constitute a design review or engineering analysis of your system. These items were noticed during an inspection of your fire protection system performed in accordance with NFPA 25 but are not part of the NFPA 25 inspection. [CONTRACTOR] makes no guarantee or assurance that any or all design or engineering defects or deficiencies have been detected. The above statement should be reviewed by your lawyer as we are not lawyers and only offer the above as example of concept. Top Myers RelMark Group 961 Pottstown Pike Chester Springs, PA 19425 610-321-2415 X-219 Cell 610-952-0965 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Charles Thurston Sent: Tuesday, August 23, 2011 6:01 PM To: [email protected] Subject: Horror Stories Hello Sprinklerforum, I am looking for stories of how an inspector doing an inspection per NFPA 25 made an "engineering" call and got the company in trouble. I need these to show my boss as to why we do not do this.... -- Best regards, Charles mailto:[email protected] Confidentiality Notice: This e-mail message, including any attachments, is for the sole purpose of the intended recipients and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender by reply e-mail and destroy all copies of the original message. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum