Try 8.16.1.6.2 in NFPA 13 (2010).
John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO 64131 | ph 816-997-7213 |
[email protected]
From: "Travis Mack, SET" <[email protected]>
To: [email protected]
Date: 09/06/2011 01:48 PM
Subject: in-rack control valves
Sent by: [email protected]
I seem to recall that you could have 20 or fewer rack sprinklers come
off the overhead system without a separate riser. Is that still
allowed? If so, can anyone provide the section of NFPA 13 where it is
allowed?
Thanks in advance.
--