It's not a Code requirement, just an idea to solve the original problem. Wait 
to install antifreeze until after the test valve. 


At 02:24 PM 9/12/2011, you wrote:
>Interesting! I am not able to find it in the 2010 NFPA 13; the requirements
>of installing isolation or check valve above the test and drain to isolate
>the antifreeze from a system during an inspectors flow test. 
>Any directive as to this being a code requirement will be appreciated.
>
>-----Original Message-----
>From: sprinklerforum-boun...@firesprinkler.org
>[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Douglas Hicks
>Sent: Sunday, September 11, 2011 9:44 AM
>To: sprinklerforum@firesprinkler.org
>Subject: Re: Antifreeze system
>
>  Yes, the BFV is in addition to and after the backflow valve.
>
>-----Original Message----- 
>From: Todd - FPDC
>Sent: Sunday, September 11, 2011 3:50 AM
>To: sprinklerforum@firesprinkler.org
>Subject: Re: Antifreeze system
>
>Is the butterfly valve in addition to the valves on the backflow. If so, 
>why?
>
>I assume you have a riser manifold or something similar with a flow switch 
>and test valve. I would install a check valve above that to be the start of 
>the antifreeze. Don't forget to install a drain above the check as well.
>
>Sent from my iPhone
>
>On Sep 11, 2011, at 3:32 AM, "Douglas Hicks" <fire...@eoni.com> wrote:
>
>> I  have a wet sprinkler system where the entire sprinkler system is filled
>
>> with antifreeze.  The riser comes from the floor, makes a 90 * into a 
>> backflow device,  to a butterfly valve, then to the attic.  The inspectors
>
>> test valve tees off the riser to the attic.  My concern is the possible 
>> loss of antifreeze when opening the inspectors test valve.  Is my concern 
>> warranted?  Or should I move the inspectors test valve to a location 
>> between the backflow device and the butterfly valve?
>> -------------- next part --------------
>> An HTML attachment was scrubbed...
>> URL: 
>>
><http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
>s/20110911/bb8dc583/attachment.html>
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@firesprinkler.org
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>_______________________________________________
>Sprinklerforum mailing list
>Sprinklerforum@firesprinkler.org
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
>
>_______________________________________________
>Sprinklerforum mailing list
>Sprinklerforum@firesprinkler.org
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
>
>__________ Information from ESET NOD32 Antivirus, version of virus signature
>database 6457 (20110912) __________
>
>The message was checked by ESET NOD32 Antivirus.
>
>http://www.eset.com
> 
> 
>
>__________ Information from ESET NOD32 Antivirus, version of virus signature
>database 6458 (20110912) __________
>
>The message was checked by ESET NOD32 Antivirus.
>
>http://www.eset.com
> 
>
>_______________________________________________
>Sprinklerforum mailing list
>Sprinklerforum@firesprinkler.org
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to