Here is an old thread
that came close, but did not answer
a question I had...


2010 NFPA 20
1 diesel, 2 electric Fire Pumps
4? jockeys
deluge systems, high-rise systems, DIPA systems,

It is understood that pump pressure sensing lines will be plumbed
between last check valve and last control valve, which are different
locations for JP versus FP.   But is it OK, per NFPA, to use pressure
sensing lines for FP's that ARE redundant that come from the same tap?
I don't see where a violation is at.  Thoughts on best practices
warmly accepted.

-- 
Scot Deal
Excelsior Fire/Al Ilham Engineering Consultants
gsm:  +968 952 87345
(go Eagles)



Date: Fri, Jun 10, 2011 at 1:47 AM
Subject: RE: Pump, Tank, 1000 ft suction line.....


... Naturally they had the sensing lines coming off a common point, and
while the sensing lines are to come off between the discharge check and gate
on either pump, the check is supposed to be on the pump side; these guy
installed the gate, then the check- then the sensing line T.