I believe Each and Every Pump for Fire Protection service is supposed to be
able to function completely independently
from Each and Every other pump. This requires sensing lines that are
independent from each other.

On Wed, Sep 21, 2011 at 10:57 PM, å... .... <[email protected]> wrote:

> Here is an old thread
> that came close, but did not answer
> a question I had...
>
>
> 2010 NFPA 20
> 1 diesel, 2 electric Fire Pumps
> 3 jockey pump
> *** 6 pumps, 6 controllers ***
> demand:  deluge systems, high-rise systems, DIPA systems,
>
> It is understood that pump pressure sensing lines will be plumbed
> between last check valve and last control valve, which are different
> locations for JP versus FP.   But is it OK, per NFPA, to use pressure
> sensing lines that come from the same tap when used for FP-that-are-
> redundant?  I don't see where a violation is at.
>
> **to add more fuel to the fire...
>    there are 8, yes 8, PRedV's downstream of the FP's.
>    Intention there was to avoid changing original POOR design practice of
>    overpressurizing feed mains (the overdesigned pressure was in order
>    to deliver at top  of standpipes in a tower.
>
>    I expect serious jockey pump cycling, if not continuous JP operation,
>    because of these PRedV's.  Client doesn't know what they are getting.
>    Apparently, neither do the designers.
>    Client may recognize this thread and get mad at me.  I hope so.  It may
>    take rage to elevate design to a higher stage.  If that is
>    what it takes, then my mission is accomplished.
>
>    Due to the authority
>    and respect of this forum (not a plug at any one member per se, but the
>    institution of this FORUM as a medium),  the client may give
> credibility
>    where previously, the designers were able to ignore well-intended-and-
>    successful-long-term-strategies for choices-that-are-easiest-for-they-
>   (the designers) to deliver.  These choices, however Code complying,
>   surrender the client's assets to head-aches, redesign, change-orders
>   and delays.   ****
>
>
> --
> Scot Deal
> Excelsior Fire/Al Ilham Engineering Consultants
> gsm:  +968 952 87345
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110922/cfd69484/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110922/d47e52b4/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to