Cory, The questions would include, assuming this is a dry pipe sprinkler system in accordance with NFPA 13: 1) what orifice size are the sprinklers in the system, and 2) where does NFPA 13 allow the use of more than one orifice for a single dry system?
Scott Futrell, PE, FSFPE, CFPS, SET (763) 425-1001 Office (612) 759-5556 Cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Cory Power Sent: Tuesday, October 04, 2011 4:48 PM To: [email protected] Subject: Re: Equiv Orifice for OH Inspectors Test The reason I'm asking is because it is an ordinary hazard system and in the plans they spec the inspectors test routing to a hub drain in a janitors closet. It would be much easier to have one 11.2k orifice above the hub drain than two 5.6 k's. -- Cory Power P& P Sprinklers Ltd 6 Main Rd Chapel Arm, NL A0B 1L0 Ph: (709) 592-2029 Fax: (709) 592-2019 On 10/4/2011 6:07 PM, Justin Reid wrote: > The Q=k*sqrt(p) math says that it should be equal flow with equal pressure. > I guess you would have slightly less pressure with the 11.2 since there is > more flow(friction). > > I just had an issue yesterday trying to get a flow valve to trip with a > remote test (one head) and thought the same thing (to look at using two > heads). > > Good luck, > > Justin Reid > > > > > On Tue, Oct 4, 2011 at 1:13 PM, Cory Power<[email protected]> wrote: > >> Just wondering if anyone have used an 11.2 K Orifice to substitute for two >> 5.6 k heads on an OH1 Dry Inspectors test? Shouldn't it be equivalent? >> >> -- >> Cory Power >> P& P Sprinklers Ltd >> 6 Main Rd >> Chapel Arm, NL A0B 1L0 >> Ph: (709) 592-2029 >> Fax: (709) 592-2019 >> >> -------------- next part -------------- >> An HTML attachment was scrubbed... >> URL:<http://fireball.**firesprinkler.org/mailman/** >> private/sprinklerforum/**attachments/20111004/c48f4ae4/**attachment.html<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111004/c48f4ae4/attachment.html> >> ______________________________**_________________ >> Sprinklerforum mailing list >> Sprinklerforum@firesprinkler.**org <[email protected]> >> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> >> > -------------- next part -------------- > An HTML attachment was scrubbed... > URL:<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111004/53f36606/attachment.html> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111004/655dd34b/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum