What is the proper procedure for stand pipes when there is no access to the 
roof?  I have an apartment building that requires a class I stand pipe.  The 
building is a 13R occupancy.  NFPA 14 states:
7.3.2* Class I Systems. Class I systems shall be provided with 2 1⁄2 in. (65 
mm) hose connections in the following locations:
(5)*At the highest landing of stairways with stairway access to a roof, or on 
roofs with a slope of less than 4 in 12 where
stairways do not access the roof.
Normally, I have always (that I recall) had roof access in one form or another. 
 The roof slope on this building is 4.5 in 12, so I am assuming than that I 
don't need to anything special with this so long as I have connections at the 
highest landing, which I do.  Do I need to do anything for testing?  I will 
have a 2-1/2" express drain on the riser that is the combination.