Todd,

See if they can give you the pallet manufacturer information and see if the 
manufacturer has done any fire testing on the pallets.  You need the Heat 
Release Rate to compare to standard pallets and plastic pallets to develop the 
correct protection. Otherwise contact UL, Tyco, Viking, or Reliable and see if 
they've tested them and if they'll tell you anything about them (e.g., they 
burn like...).

Scott Futrell
 
(763) 425-1001 Office
(612) 759-5556 Cell

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd - FPDC
Sent: Tuesday, October 11, 2011 10:49 AM
To: [email protected]
Subject: Particle board pallets

I'm in a facility and am staring at a stack of particle board pallets. The same 
material that you can get at Home Depot, but moulded into the shape of a 
pallet. No openings. Probably similar to plastic pallets in design  Thoughts on 
protecting? 