Yes, we have done many combined Private domestic and private fire water pump 
stations. When you start to look at such a pump station you need to develop 
design parameters for all domestic and plant usage along with fire water 
demand. You need to determine with a great degree of confidence the domestic 
and plant process usage and specific time line of process water demand and 
domestic water demands; such as when and where the process water is required 
and at what flows, what are the operating parameters for the plant workers and 
what are the shift and break times since at breaks and meal times domestic 
water usage is much greater than during normal operating times. Does  the plant 
have a dining facility and what type of equipment is being used.

Once you have determined the domestic flows and when and where they occur you 
then need to sit down with the end user to determine their needs. What type of 
pressure is required for the process equipment, domestic water devices, flush 
type or tank type, grass irrigation system, etc., once you sit down with the 
end user (not the client's engineer but plant operations personal who are 
operating the facility) you need to determine if multiple smaller domestic 
service pumps are required in order to have the system operate in an 
economically and technically sound manner. Having a 2,500 gpm domestic water 
pump turning itself on and off to provide make up water is not economically 
sound. It is more reasonable to have 4 or 5 smaller pumps in parallel, with 
start and stop controlled by a 4x or 5x pump controller which monitors the 
pressure on the combined system to sequentially start the pumps based on system 
water pressure. You will also need a device to handle the pressure surges from 
the pumps starting and stopping, On the systems that I have designed I have 
used a 500 gallon hydro-pneumatic bladder tank to handle the pressure surge. 
However the hydro-pneumatic size needs to be determined based on the final 
system design. The fire pump start pressure is set based on sprinkler system 
design parameters and the domestic systems design parameters. 

There is more to this contract and design than meets the eye and the SFMO's 
blessing does not mean a thing since the SFMO has no liability to the client 
only you have the liability and it will be for the sprinkler and domestic water 
pumps since there appears to have been no engineering based on the operational 
needs of the facility. Just because it meets the code does not mean that it 
meets the clients operational needs. 

>From what you have described this project needs to be much better defined as a 
>whole since the fire protection jockey pump might be the 2,500 gpm domestic 
>service pump and since it is connected to the private service fire water main 
>it will fall into the requirements of NFPA 24 "Standard for the Installation 
>of Private Fire Service Mains and Their Appurtenances" operative word is 
>"private". Your might have to design the fire pump house  and pumping 
>equipment as a municipal water service pump station meeting both AWWA 
>requirements and NFPA requirements, example that the paint on the interior of 
>the fire pump must be AWWA certified for domestic water service use, the 
>entire pump station might have to have full emergency power back up including 
>all pumps and all power such as lights, alarms, pumping equipment, controls, 
>heating and ventilation, etc.

I have a sample drawing that I can provide you off line if you want to look at 
it for conversation. 

Have a fire safe day.              

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ted Hall
Sent: Friday, November 18, 2011 11:46 AM
To: [email protected]
Subject: Fire Pump to multi suppy

We are bidding a project where we have been given the design view from 10,000 
feet. But the contractor who is awarded the project is to complete the design. 
The project will have a million gallon storage tank to supply both fire 
sprinklers an facility water. There is to be one pump house which we would not 
be involved with that will house a 2500GPM pump at 145psi and another 500GPM 
pump at about the same PSI. The Fire Pump House will have one electric fire 
pump at 125 psi and one diesel fire pump same rating and one conversion// spare 
fire pump at the same rating. All pumps will feed from the storage tank and 
into a 12" underground loop. The schematic shows a demand of plant water which 
could be as much as 2500GPM and the fire sprinklers (ESFR system) coming off 
the same underground loop. The owner has gotten the SFMO's blessing on this 
arrangement but I am thinking I am going to be replacing fire pumps due them 
starting and not shutting off. No way a jockey pump can keep up 
 with the demand of the plant water. Has anyone ever been involved with this 
configuration before. I am thinking it isn't even code.

Ted Hall,  CET
NICET 119535 Water Based {Formerly AutomaticSprinkler}
Systems Layout Level III
Sentinel Fire Protection 2040 Westland Dr. S.W.
Cleveland, Tn. 37311 Office 423 476-7570
Fax 423 476-9014
[email protected]


-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111118/a138b5b6/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to