Tom:

Don't know what building code this I-2 is under, but assuming it is the
IBC, see 2009 edition, Section 407.5, which requires a system per 903.3.1.1
throughout smoke compartments containing patient sleeping rooms.  903.3.1.1
is a 13 system.  Also see 903.2.6 which requires an automatic sprinkler
system throughout buildings with a Group I fire area.  It then says I-1 can
be 13R or 13D, implying that all other Group I occupancies must be 13.

*Dave*



On Mon, Dec 12, 2011 at 5:17 PM, Don Lowry <[email protected]> wrote:

> Don't think an I2 can be installed as 13R.
>
> Don
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Tom Duross
> Sent: Monday, December 12, 2011 5:04 PM
> To: [email protected]
> Subject: Changing Code Standards in an Existing Bldg.
>
> This is kind of a rant/long winded digression/request for opinion kinda
> thingy..
> I have a group residence built in the late seventies with a dry system.
> I-2, ranch style building with attic.
> Steel pipe, attic and living space coverage, 13 design (closets, bathrooms,
> concealed spaces, everything covered).
> I've mentioned it to this forum before.   The dry system has become a real
> source of frustration this past month.
> When we did our annual testing this summer all went well.  This is our 3rd
> year here so we did a full flood trip.
> Been fine as far as I know since August.  This past Saturday it tripped.
> When I got there, reset it, noticed air pressure dropping and air
> compressor
> cycling every 30 minutes.
> I climbed into the attic (more like lumbered) and found several locations
> of
> pinhole leaks in the underside of mains.
> This is old 2 1/2"-3"-4" threaded pipe sitting on the bottoms of the
> trusses.  Great.
> With it being a Saturday afternoon, the supply house is closed.
> I managed to find a couple of plumbing supply houses ready to close and
> bought three saddle type repair clamps.
> Went back and installed them and once back up, the cycling dropped to about
> every 90-100 minutes for about a 20 minute run.
> I tightened up the differential on the pressure switch so it ran for only
> 3-4 minutes but it started every 45 minutes or so.
> I felt that better since it was a riser mount and got hot in that 20 minute
> cycle.
> The clients were all still out at a day program and needed to return,
> feeling for them as I do I told the manager to bring them home.
> I called the Deputy, told him I did a temporary patch and fix for the
> weekend, pretty sure it would be OK, and would return Monday.
> I returned Monday morning, still cycling every 45 minutes or so, squeezed
> back up (with some lights this time!) and found one more.
> Right under the pipe, as you slide your hand along the pipe, just a little
> hiss of air.  I had brought gas leak detector with me in a spray bottle.
> I sent baby brother out for another repair saddle (I just wanted to get it
> tight first) while I balanced across 24" OC roof joists with a trouble
> light
> in one hand and a flashlight in my mouth.  I sprayed every fitting I could
> see, even the high uprights, no bubbles.  We put the 2" saddle on,
> compressor started and stopped, we sat there in the attic for over an hour,
> quiet as church mice.  About ready to get up and pat each other on the
> back,
> the air compressor started again. UUGH!  We climbed back down, watched the
> gauge again, sprayed half a bottle of leak detector all over the dry pipe
> valve, air supply, inspectors test, went in and sprayed the faces of the
> dry
> pendents.  That's all that was left.  Nothing found.
> I think I'm just almost causing small leaks to appear after I stop the
> larger ones.  Almost chasing my own tail (if I had one).
> Remember Curly standing in the bathtub putting one section of pipe into
> another and the water won't stop?  Am I a victim of circumstance?
>
> Well, it's still this way as I write this and thinking of options for the
> Owner, I wanted to (get to the point Tom) run something by the forum.
> I'm past the point of no return weather-wise, I don't want to flood it.  It
> was 28 degrees last night.
> What if I pumped glycol (I know, I know) to not only maybe find a drip but
> maybe to stabilize it for the winter?  Has anyone done this?
> The other question, and the reason behind the title, could I just abandon
> the dry system?
> Could I just change the system from a '78 NFPA 13 dry system to a '07 13R
> in
> an existing building that's already sprinklered?
> The attic isn't used for living purposes, storage, has no mechanical
> equipment or anything serviceable.  Just an 18x18 access panel.
> I think if it wasn't sprinklered and I was asked to install a system,
> that's
> what I'd do.  A soffitted wet system with sidewalls.
>
> Scratching my head and removing splinters.
>
> TD
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111212/86c8047c/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to