And compressor piping, but you've already done that, right?
Shutting off the control valve from the air supply to limit the leakage at trim?


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jim Davidson
Sent: Tuesday, December 13, 2011 9:15 AM
To: [email protected]
Subject: RE: Changing Code Standards in an Existing Bldg.

Tom, 

I would also check the valves on the test connections and drum drips for 
leakage around the valve seat.

Have a fire safe day.

Jim Davidson 
 
Davidson Associates
Fire Protection * Medical Gas * Code Consulting
302-994-9500   Fax:302-234-1781


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Tom Duross
Sent: Monday, December 12, 2011 6:16 PM
To: [email protected]
Subject: Changing Code Standards in an Existing Bldg.

This is kind of a rant/long winded digression/request for opinion kinda thingy..
I have a group residence built in the late seventies with a dry system.
I-2, ranch style building with attic.
Steel pipe, attic and living space coverage, 13 design (closets, bathrooms, 
concealed spaces, everything covered).
I've mentioned it to this forum before.   The dry system has become a real
source of frustration this past month.
When we did our annual testing this summer all went well.  This is our 3rd year 
here so we did a full flood trip.  
Been fine as far as I know since August.  This past Saturday it tripped.  
When I got there, reset it, noticed air pressure dropping and air compressor 
cycling every 30 minutes.
I climbed into the attic (more like lumbered) and found several locations of 
pinhole leaks in the underside of mains.
This is old 2 1/2"-3"-4" threaded pipe sitting on the bottoms of the trusses.  
Great.
With it being a Saturday afternoon, the supply house is closed.
I managed to find a couple of plumbing supply houses ready to close and bought 
three saddle type repair clamps.
Went back and installed them and once back up, the cycling dropped to about 
every 90-100 minutes for about a 20 minute run.
I tightened up the differential on the pressure switch so it ran for only
3-4 minutes but it started every 45 minutes or so.
I felt that better since it was a riser mount and got hot in that 20 minute 
cycle.
The clients were all still out at a day program and needed to return, feeling 
for them as I do I told the manager to bring them home.
I called the Deputy, told him I did a temporary patch and fix for the weekend, 
pretty sure it would be OK, and would return Monday.
I returned Monday morning, still cycling every 45 minutes or so, squeezed back 
up (with some lights this time!) and found one more.
Right under the pipe, as you slide your hand along the pipe, just a little hiss 
of air.  I had brought gas leak detector with me in a spray bottle.
I sent baby brother out for another repair saddle (I just wanted to get it 
tight first) while I balanced across 24" OC roof joists with a trouble light in 
one hand and a flashlight in my mouth.  I sprayed every fitting I could see, 
even the high uprights, no bubbles.  We put the 2" saddle on, compressor 
started and stopped, we sat there in the attic for over an hour, quiet as 
church mice.  About ready to get up and pat each other on the back, the air 
compressor started again. UUGH!  We climbed back down, watched the gauge again, 
sprayed half a bottle of leak detector all over the dry pipe valve, air supply, 
inspectors test, went in and sprayed the faces of the dry pendents.  That's all 
that was left.  Nothing found.
I think I'm just almost causing small leaks to appear after I stop the larger 
ones.  Almost chasing my own tail (if I had one).
Remember Curly standing in the bathtub putting one section of pipe into another 
and the water won't stop?  Am I a victim of circumstance?

Well, it's still this way as I write this and thinking of options for the 
Owner, I wanted to (get to the point Tom) run something by the forum.
I'm past the point of no return weather-wise, I don't want to flood it.  It was 
28 degrees last night.  
What if I pumped glycol (I know, I know) to not only maybe find a drip but 
maybe to stabilize it for the winter?  Has anyone done this?
The other question, and the reason behind the title, could I just abandon the 
dry system?
Could I just change the system from a '78 NFPA 13 dry system to a '07 13R in an 
existing building that's already sprinklered?
The attic isn't used for living purposes, storage, has no mechanical equipment 
or anything serviceable.  Just an 18x18 access panel.
I think if it wasn't sprinklered and I was asked to install a system, that's 
what I'd do.  A soffitted wet system with sidewalls.

Scratching my head and removing splinters.

TD

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to