Without knowing what edition of 13 and what building code, I'd be calc'g one 
row of heads the length of your remote area at .3gpm/linear foot, adding it to 
the calc for the OH system.
In the small rooms, pick up .3GPM/linear ft for the heads in that room.

I think you were on the right track.

I'm taking a different approach in one today, excluding it cause I'm in 
conceptual stage (25% dwgs) and can.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Monday, December 19, 2011 12:26 PM
To: [email protected]
Subject: Water curtains

We have an engineered design (by a registered PE) that has a glass atrium wall 
in  a LEEDS building. I am assuming some of you guys have already dealt with 
this. He has called for SSP heads  - not listed window sprinklers - on both 
sides of the wall.

He is fuzzy in his logic for calculating them however and frankly so am I.
One side is 3 floors of glass so it is one huge compartment, the other side is 
split into offices, so there are only 1-3 window sprinklers in each room.

How do we calc the atrium on the big room side - as a water curtain balanced 
with the OH system?

In the small rooms, do we just do a most demanding room calc and include the 
window sprinklers?

Thanks for the help.
Greg

--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111219/63ce58f2/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to