But you can you can reduce the area by using EC sprinklers
* For HC-2 and HC-3 occupancies with ceilings up to 30 ft (9 m), reduce sprinkler design demand to 0.3/1500 (gpm/ft2)/ft2 (12/140) (mm/ min)/m2 for wet-pipe systems when using K11.2EC (K160EC) upright sprinkler with temperature ratings of 160°F (70°C). * For HC-2 & HC-3 occupancies with ceilings up to 30 ft (9 m), reduce sprinkler design demand to 0.3/1000 (gpm/ft2)/ft2 (12/90) (mm/ min)/m2 for wet-pipe systems when using K14.0EC (K200EC) upright sprinkler with temperature ratings of 160°F (70°C). * Although the sprinkler system protection guidelines use density over demand area as a design format, when using extended coverage sprinkler in facilities with ceilings up to 30 ft (9 m) high ensure the number of sprinklers does not drop below a minimum of 6 sprinklers for K11.2EC
(K160EC) and 4 sprinklers for K14.0EC (K200EC).

David M. Canham
Fire Systems Solutions
15 Sayles Avenue
Lincoln, RI 02865
401-725-1089

-----Original Message----- From: A.P.Silva
Sent: Monday, December 19, 2011 2:58 PM
To: [email protected]
Subject: FM requirement


Does FM allow design area reduction for QR sprinklers?

I know I should look for the answer in the FM data sheets, which I will do
when I get the time. But if anyone knows or have come across it recently,
would be a great help. From what I remember, FM does not allow it, but it's
been awhile since I've done an FM design.

Tony

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to