As per NFPA 25 the contractor is NOT RESPONSIBLE to DIAGNOSE DESIGN 
DEFICIENCIES that IS THE OWNER'S responsibility. NFPA 25 is written in a way to 
limit the sprinkler contractor's liability if the contractor follows the 
inspection testing and maintenance procedures as outlined in NFPA 25. I am 
surprised that sprinkler contractors keep trying to take on more and more 
liability by trying to be all things to all clients. At some point your 
liability insurance carrier might say "you are practicing engineering and we 
are not covering you for "Errors and Omissions". This just happened in New 
Jersey with a Mechanical Contractor who was installing fire sprinkler systems, 
was sued by an owner. The insurance company reviewed his application for 
liability insurance coverage and found that the contractor did not inform the 
insurance company that the contractor was installing sprinkler systems, the 
insurance company tried to decline coverage as the case was winding its way 
through the court system. 

If you think there is a problem with the standpipe system express your concerns 
to your client in a separate letter not related to your inspection survey 
report. Make it very clear in your letter that you are only expressing your 
opinion and that the Owner needs to get a qualified Professional engineer to 
assist the owner in the review. For more info go to Top Myers' RelMark's web 
site www.relmark.net and review the court cases. 

Have a fire safe New Year!!

Regards         

Jim

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Friday, December 30, 2011 3:45 PM
To: [email protected]
Subject: RE: NFPA 25 standpipe test

But it is required in the new edition and there is an inference in the
standards and generally an expectation of due diligence in prosecuting
one's work both under 25 and in general.  25 has left a bit of a void
regarding the contractor's responsibility to diagnose design
deficiencies (not required and the remedy for deficiencies clearly being
outside the scope) and general deficiencies (implied to be within the
scope), and it doesn't contain any reference to having multiple design
bases in the same building or system.   The contractor is not
responsible for the design but needs to test according to what's there
(I'm paraphrasing) but if there is incongruence at any level you have to
use your best judgment.  I would seize this opportunity to flow test the
systems, catalog their performance potential and sign the FDC's as such.

To Roland and Jim's comments, I think Meridian One has drawn attention
to this issue; in the case of SFFD they have been trying to fight fires
on super-steep hills since before the turn of the 20th century.  That FD
has been very progressive on standpipes because they have to be - you
can't park an engine closer than a block away from many buildings in
that city and pumping up hill as well as up the building to firefighters
is the norm there, so they are very sensitive to hose-end pressures.
Meridian One - especially the USFA report that followed - has given us
push forward in advocating higher working pressures and amending 14 to
allow performance based designs for both primary and secondary water
supplies.

As for pipe dreams, ask the firefighters who are expected to go into
that building if knowing what their water supply will be is a pipe
dream.   Time to raise the bar of expectations and I have had more than
one emphatic conversation with a building owner on that subject.   Tell
them to put a big sign on the FDC instead that says, "Attention
Responders: We do not know what residual pressures you will have at the
Class 1 standpipe connections in this building.   Proceed with caution."

My opinion only,

Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson,
Duane (NIH/OD/ORS) [C]
Sent: Friday, December 30, 2011 8:52 AM
To: [email protected]
Subject: RE: NFPA 25 standpipe test

One more piece of information to ponder...If the standpipe system is
designed as a manual wet standpipe, the 5 year flow test is not required
per NFPA 25:6.3.1 2008 ed. The flow test is only required for automatic
standpipe systems. Not sure if this applies to your situation?

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"

-----Original Message-----
From: Todd Williams [mailto:[email protected]] 
Sent: Friday, December 30, 2011 10:50 AM
To: [email protected]
Subject: RE: NFPA 25 standpipe test

Steve,

That's a great pipe dream and would work well in a place as
sophisticated as SF or LA, but this is a small city hospital. This AHJ's
response to everything (besides 'what do you want in your coffee') is to
do it per NFPA. Cooperation and coordination are probably going to
minimal. I can't even verify right now if a proper standpipe acceptance
test was done when the system was installed. So far, they, the owner,
the insurance company and whatever agency the reports have been sent to
has accepted the 9 single standpipe tests at 65 psi with max water
flowing about 600 gpm, back to at least 2000. That is going to require
re-education on a massive scale with little, if any compensation for it.

This is not a project I am involved with. I am just answering a question
from a client regarding a letter the insurance company asked for.



At 09:43 PM 12/29/2011, Steve Leyton wrote:
>I was trying to stay away, I really was, but Geo's e-mail is a great
segue ...
> 
>It is a great time to see what the system(s) will actually produce at
different inlet pressures.   And to add signage to the FDC(s) that tell
the responding engineer what to pump in order to get whatever GPM and
PSI are to be delivered at the referenced outlets.   If you have both
65psi and 100psi era Class I standpipes, you can definitely work with
the AHJ to come up with a mutually satisfactory methodology for testing
and performance.   Verify with the AHJ what types of nozzles or tips
they use or carry for attack lines what the minimum good working
pressure is for each.  If the systems are built with standard weight
fittings and valves, then see what you can get out of the remote
standpipe at 175psi inlet pressure and call it a day, unless the
performance is so grossly inadequate as to cause concern for the AHJ, in
which case you have what is known in technical terms as a SNAFU.
> 
>As an example of how at least one FD has grown to address this wide
range of standpipe performance (sometimes in the same building), City of
San Franciso trucks and engines carry three different types of tips.  If
the ones fitting to the hose packs aren't right for a particular fire,
they can go all the way down to low pressure smooth bore or straight
stream.   But it starts with knowing what's gonna come out and the
signage is now a prescriptive requirement of both 13 and 14, and which
can be easily retrofitted.
> 
>SML
>
>________________________________
>
>From: [email protected] on behalf of George 
>Church
>Sent: Thu 12/29/2011 12:26 PM
>To: [email protected]
>Subject: RE: NFPA 25 standpipe test
>
>
>
>Todd-
>If the intent of NFPA 25 and this test is to confirm the stuff actually

>works, it might be a great time to find out what the pipe scheduled
standpipes will produce- Better to know soon, rather than find out when
there's a fire in an unsprinklered area (since that's the same area
where these old standpipes will be, Murphy's Law of Cascading
Catastrophes) what the FD can expect to get out of these, and if they
blow apart or not.
>
>
>George L.  Church, Jr., CET
>Rowe Sprinkler Systems, Inc.
>PO Box 407, Middleburg, PA 17842
>877-324-ROWE       570-837-6335 fax
>[email protected]
>
>
>
>-----Original Message-----
>From: [email protected]
[mailto:[email protected]] On Behalf Of Todd
Williams
>Sent: Thursday, December 29, 2011 2:59 PM
>To: [email protected]
>Subject: Re: NFPA 25 standpipe test
>
>Exactly what I am dealing with. Quite honestly, if I saw something that
said flow the most remote hose outlet, I would only flow one outlet at
250 gpm. I would not from that surmise that they wanted to recreate an
acceptance test, if one was ever done. The hospital dates from at least
1912, although I don't know when each section was built. There was a
major expansion in 2005 when they added a second fire pump and increase
the area by about 40%.
>
>So would the correct procedure be to go through and date each standpipe
and figure out how each was sized. Those that are pipe schedule could be
left alone, the pre 1993 need to be tested to 1250 gpm (partially
sprinklered) and 65 psi at the top outlet and those from 2005 tested at
1000 gpm (fully sprinklered) at 100 psi?
>
>Is there anything other than handbook commentary that details exact
testing procedures? We are using 2002 standards.
>
>
>
>At 10:12 AM 12/29/2011, you wrote:
>>The confusion started when 25 said flow the most remote hose
>>connection.  Some focused on the fact that it used the singular tense
>>verses plural so obviously they only had to flow from ONE outlet and
>>since an outlet only has to flow 250 gpm THAT was the amount to flow
>>for the test.  DOH!
>>
>>Roland
>>
>>On Dec 29, 2011, at 6:14 AM, Todd Williams wrote:
>>
>>>I am working with a hospital with a total of 9 standpipes. There are
>>>standpipes that are both pre and post 1993. The original building is
>>>partially sprinklered and the new section is fully sprinklered.
>>>
>>>1. Is the intent of NFPA 25 that multiple standpipes be flowed
>>>simultaneously to meet the 1250 gpm demand?
>>>
>>>2. Should the two sections of the hospital be flow independent of
each
>>>other?
>>>
>>>3. If yes to 1 and 2, could the new section be flowed as a fully
>>>sprinklered building (thus 1000 gpm) as opposed to 1250?
>>>
>>>4. How should i handle pipe schedule standpipes, if any exist?
>>>
>>>I haven't had to deal with 5 year standpipe tests before.
>>>
>>>Todd G. Williams, PE
>>>Fire Protection Design/Consulting
>>>Stonington, CT
>>>860.535.2080
>>>www.fpdc.com
>>>
>>>_______________________________________________
>>>Sprinklerforum mailing list
>>>[email protected]
>>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>-------------- next part --------------
>An HTML attachment was scrubbed...
>URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20111229/accee849/attachment.html>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum