These limitations need to go away. They're based on pipe schedules, and not
because the limitations are true , but merely because the schedule stops at
400 heads. In the days when schedules were developed 52K was a really big
building.

On Mon, Jan 2, 2012 at 10:48 AM, Matt Grise <[email protected]> wrote:

> Now that FM allows 60ksf, I have had more success convincing AHJ's that
> sprinkler systems still work when they exceed 52K.
>
> Matt Grisé PE*, LEED AP
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.927.0222 cell
> www. AFPsprink.com
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Todd - FPDC
> Sent: Monday, January 02, 2012 12:46 PM
> To: [email protected]
> Subject: Re: 52,000 square feet
>
> Chris, I agree is that is what the Code says. However, the 52000 is an
> arbitrary number and has no real impact on protection. For a couple of
> thousand square feet, I wouldn't have a big problem suggesting it. Probably
> 3k max.
>
> Sent from my iPhone
>
> On Jan 2, 2012, at 12:46 PM, "Cahill, Christopher" <[email protected]>
> wrote:
>
> > As a former AHJ many requests, all denied with I agree it's silly but
> it's the law.
> >
> > As a former contractor wanted to make such requests but never did
> because it's not compliant with the law.
> >
> > As a current consultant would only make such request if specifically
> instructed by the client over my clearly documented objections. (with the
> hope the AHJ would back the law)
> >
> > And I don't think one can put a 52,000 sq.ft. aux dry system off a
> 52,000 sq.ft. wet system as an example.  The combined systems are still
> limited to 52,000 sq.ft.  So adding a control valve and flow switch at the
> additions off the existing isn't going to help.
> >
> > As any role would suggest if you can easier cut off 6,000 sq.ft. near
> the riser and turn that into its own system.  Avoids the long run and then
> add the new 6,000 to the end.
> >
> > Chris Cahill, PE*
> > Senior Fire Protection Engineer
> > Aviation & Facilities Group
> > Burns & McDonnell
> > P:  952.656.3652
> > F:  952.229.2923
> > [email protected]
> > www.burnsmcd.com
> > *Lic. in MN
> >
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> [email protected]] On Behalf Of Bob
> > Sent: Monday, January 02, 2012 11:31 AM
> > To: [email protected]
> > Subject: RE: 52,000 square feet
> >
> > Greg,
> > I think that option two would be ok.  It seems that it's ok to have an
> auxiliary dry system off the end of a wet system, so an auxiliary wet
> system should work as well.
> >
> >
> >
> > Bob Knight, CET III
> > 208-318-3057
> > www.firebyknight.com
> >
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of Greg
> McGahan
> > Sent: Monday, January 02, 2012 10:04 AM
> > To: [email protected]
> > Subject: 52,000 square feet
> >
> > We have a school that is getting 2 small additions at the end of the
> wings of approx. 6,000 and 3,000 sqft respectively. If we tried to tie on
> to the end of one system to feed the larger addition, that system would be
> approximately 56,000 sqft. Th other two options (I guess) would be to run
> 250' of 3" back to the main riser and create a new system for this
> addition, or use it for both additions with another 300' or so of main, or
> maybe to put in a new control valve and flow switch at each addition to
> supply them.
> > I am not sure if the second option would meet the intent of the code and
> I am too confused to figure this out this early in the year.
> >
> > The other addition appears to be on a system that is already about
> 53,000 sqft and adding the addition would also put it around the 56,000
> mark.
> >
> > Has anybody ever asked for a variance on something like this? It
> honestly doesn't make any sense to put it in a separate system (other than
> to meet
> > code) because the operation of the system will not actually be effected.
> > Especially in the way these systems are shaped, there are several
> different fire rated zones of much smaller area.
> >
> > Happy New Year and thanks,
> >
> > --
> > Greg McGahan
> > Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> > 1160 McKenzie Road
> > Cantonment, FL 32533
> > 850-937-1850
> > fax 850-937-1852
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL:
> > <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
> > s/20120102/1eb1176e/attachment.html>
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > -----
> > No virus found in this message.
> > Checked by AVG - www.avg.com
> > Version: 2012.0.1901 / Virus Database: 2109/4718 - Release Date: 01/02/12
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120103/c5838ccd/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to