I think they should go away or at least be more consistent. We are allowed to 
have more than 52k/40k in certain case. We can have a 52k sqft. system with a 
30k sqft. mezzanine on one valve. 40k sqft. above and 40k sqft. below on one 
valve. Multiple floors (6  stories with 52k on each floor) on one valve. We 
just can't have 54k sqft. on one valve on the same level.


Ron Fletcher
Aero Automatic
Phoenix, AZ


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Tuesday, January 03, 2012 8:38 AM
To: [email protected]
Subject: RE: 52,000 square feet

I'm not sure I agree they need to go away.  I understand they didn't exactly 
come from a well thought out principal based on some scientific merit.  But my 
reasoning goes like this.  In a 208,000 sq.ft. building right now we would have 
4 systems.  If a system is down for maintenance or say to add a head in a new 
office there is a 75% chance the fire will start in a sprinklered area.  And 
yes I have been involved with two buildings where the system was off when the 
fire started.  Get rid of the limits and there is a 100% chance the fire starts 
in an unsprinklered area during these same down times.  Double the current 
limits and it's 50/50.   Remember most work is in design build which almost 
always = lowest bid = one system per building. 

Sure make the argument some places will have thoughtful engineers, thoughtful 
contractors, or owners that are interested in issues like this and I won't 
argue but what about the majority of work.  Modify the limits perhaps but they 
shouldn't go away.  Maybe something like warehouses 100k, HPS 40k, single 
tenant office buildings 50k, lease office 30k, malls by tenant.  By floor in 
lease or malls, building over 4 stories. 

Chris Cahill, PE*
Senior Fire Protection Engineer
Aviation & Facilities Group
Burns & McDonnell
P:  952.656.3652
F:  952.229.2923
[email protected]
www.burnsmcd.com
*Lic. in MN


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Tuesday, January 03, 2012 9:16 AM
To: [email protected]
Subject: Re: 52,000 square feet

These limitations need to go away. They're based on pipe schedules, and not 
because the limitations are true , but merely because the schedule stops at
400 heads. In the days when schedules were developed 52K was a really big 
building.

On Mon, Jan 2, 2012 at 10:48 AM, Matt Grise <[email protected]> wrote:

> Now that FM allows 60ksf, I have had more success convincing AHJ's 
> that sprinkler systems still work when they exceed 52K.
>
> Matt Grisé PE*, LEED AP
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.927.0222 cell
> www. AFPsprink.com
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Todd - FPDC
> Sent: Monday, January 02, 2012 12:46 PM
> To: [email protected]
> Subject: Re: 52,000 square feet
>
> Chris, I agree is that is what the Code says. However, the 52000 is an 
> arbitrary number and has no real impact on protection. For a couple of 
> thousand square feet, I wouldn't have a big problem suggesting it.
> Probably 3k max.
>
> Sent from my iPhone
>
> On Jan 2, 2012, at 12:46 PM, "Cahill, Christopher" 
> <[email protected]>
> wrote:
>
> > As a former AHJ many requests, all denied with I agree it's silly 
> > but
> it's the law.
> >
> > As a former contractor wanted to make such requests but never did
> because it's not compliant with the law.
> >
> > As a current consultant would only make such request if specifically
> instructed by the client over my clearly documented objections. (with 
> the hope the AHJ would back the law)
> >
> > And I don't think one can put a 52,000 sq.ft. aux dry system off a
> 52,000 sq.ft. wet system as an example.  The combined systems are 
> still limited to 52,000 sq.ft.  So adding a control valve and flow 
> switch at the additions off the existing isn't going to help.
> >
> > As any role would suggest if you can easier cut off 6,000 sq.ft. 
> > near
> the riser and turn that into its own system.  Avoids the long run and 
> then add the new 6,000 to the end.
> >
> > Chris Cahill, PE*
> > Senior Fire Protection Engineer
> > Aviation & Facilities Group
> > Burns & McDonnell
> > P:  952.656.3652
> > F:  952.229.2923
> > [email protected]
> > www.burnsmcd.com
> > *Lic. in MN
> >
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> [email protected]] On Behalf Of Bob
> > Sent: Monday, January 02, 2012 11:31 AM
> > To: [email protected]
> > Subject: RE: 52,000 square feet
> >
> > Greg,
> > I think that option two would be ok.  It seems that it's ok to have 
> > an
> auxiliary dry system off the end of a wet system, so an auxiliary wet 
> system should work as well.
> >
> >
> >
> > Bob Knight, CET III
> > 208-318-3057
> > www.firebyknight.com
> >
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of Greg
> McGahan
> > Sent: Monday, January 02, 2012 10:04 AM
> > To: [email protected]
> > Subject: 52,000 square feet
> >
> > We have a school that is getting 2 small additions at the end of the
> wings of approx. 6,000 and 3,000 sqft respectively. If we tried to tie 
> on to the end of one system to feed the larger addition, that system 
> would be approximately 56,000 sqft. Th other two options (I guess) 
> would be to run 250' of 3" back to the main riser and create a new 
> system for this addition, or use it for both additions with another 
> 300' or so of main, or maybe to put in a new control valve and flow 
> switch at each addition to supply them.
> > I am not sure if the second option would meet the intent of the code 
> > and
> I am too confused to figure this out this early in the year.
> >
> > The other addition appears to be on a system that is already about
> 53,000 sqft and adding the addition would also put it around the
> 56,000 mark.
> >
> > Has anybody ever asked for a variance on something like this? It
> honestly doesn't make any sense to put it in a separate system (other 
> than to meet
> > code) because the operation of the system will not actually be effected.
> > Especially in the way these systems are shaped, there are several
> different fire rated zones of much smaller area.
> >
> > Happy New Year and thanks,
> >
> > --
> > Greg McGahan
> > Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> > 1160 McKenzie Road
> > Cantonment, FL 32533
> > 850-937-1850
> > fax 850-937-1852
> > -------------- next part -------------- An HTML attachment was 
> > scrubbed...
> > URL:
> > <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
> hment
> > s/20120102/1eb1176e/attachment.html>
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > -----
> > No virus found in this message.
> > Checked by AVG - www.avg.com
> > Version: 2012.0.1901 / Virus Database: 2109/4718 - Release Date: 
> > 01/02/12
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120103/c5838ccd/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to