But with the separate control valves at the base of riser (as indicated in
8.16.1.6) you could protect 40,000ft² per In Rack System, correct?

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
www.keyfireprotection.com
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Wednesday, February 01, 2012 9:59 AM
To: [email protected]
Subject: Re: What's wrong with this?

There's also a nice drawing portraying it in the Handbook.

An additionally problem is that you would be likely exceeding your  
system maximum since you have now combined your two systems.  Despite  
the fact that we use to do that for hose connections but that was  
explicitly allowed and had a different function.

Roland

On Feb 1, 2012, at 3:55 AM, Bobby Gillett wrote:

> NFPA 13 2010 -  8.16.1.6 , 8.16.1.6.1, 8.16.1.6.2, 8.16.1.6.3
>
> Bobby Gillett
> Sr. Project Manager