The only time 3.5" and 5" are used is if you have to do something on an old 
pipe schedule system. Never on a new project.


At 12:04 PM 2/9/2012, you wrote:
>We use 3" on a regular basis. Do not use 3.5" at all and in fact usually end 
>up upsizing it to 4" when we encounter it in the field. 5" pipe and fittings 
>are available on a limited basis and we only use it for repairs or when we 
>absolutely need to connect to it.
>
>Mike Hill
>
>Sent from my iPhone
>
>On Feb 9, 2012, at 11:57 AM, Justin Reid <[email protected]> wrote:
>
>> I was looking at a pipe table from a sprinkler pipe manufacturer and
>> they list the following pipe sizes:  2.5", 3", 3.5" 4", 5" and 6". How
>> often do you find your company using 3" , 3.5" and 5" pipe in designs?
>> 
>> Any input would be greatly appreciated
>> 
>> Thanks!
>> 
>> Justin Reid
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com