We have had a question come up about main drain testing per NFPA 25:

In the NFPA 25 2011 handbook it states:

13.2.4 Before opening a test or drain valve, it shall be verified that adequate 
provisions have been made for drainage.

The commentary for this item includes the phrase:

In high-rise buildings with the sprinkler riser in the stairway, a separate 
drain line is often installed that is one diameter larger than the largest main 
drain valve connected to the drain line. The drain line should not be 
considered a main drain connection, but should be viewed as an auxiliary drain 
for each floor. Unlike the main drain, the auxiliary drain is not intended to 
be flow tested. The auxiliary drain line can be used to conduct flow tests on 
pressure regulating valves installed in the fire sprinkler system and in the 
fire department standpipe system, and also to test the system flow switch.

This is followed up with the testing requirements:

13.2.5* Main Drain Test. A main drain test shall be conducted annually at each 
water based fire protection system riser to determine whether there has been a 
change in the condition of the water supply piping and control valves. (See 
also 13.3.3.4.)

Additionally this annex material is presented:

A.13.2.5 Main drains are installed on system risers for one principal reason: 
to drain water from the overhead piping after the system is shut off. This 
allows the contractor or plant maintenance department to perform work on the 
system or to replace nozzles after a fire or other incident involving system 
operation.

The test for standpipe systems should be done at the low-point drain for each 
standpipe or the main drain test connection where the supply main enters the 
building.

NFPA 13 2010 Handbook states:

8.16.2.4.5 For those drains serving pressure-reducing valves, the drain, drain 
connection, and all other downstream drain piping shall be sized to permit a 
flow of at least the greatest system demand supplied by the pressure-reducing 
valve.

And the handbook expands with:

Piping controlled by sectional valves represents a significant segment of the 
sprinkler system. Sectional or floor control valves serve the same function for 
that portion of the system as the main drain does for the entire system. The 
use of express drains in high-rise nuildings is one method of disposing of 
water from upper floors. Express drains or floor drains used when the drain 
does not drain directly to the outside must be capable of handling the flow and 
not restrict it.

Is the NFPA 13 material meant only to apply to the full flow testing of 
pressure reducing valves? We have some concern that these two standards 
conflict on the idea of "express drains" when it comes to floor control 
manifolds not installed on combination standpipe risers. With a dedicated 
sprinkler riser is the intent to use a full flow main drain test at each floor 
control valve, or only at the lowest level of the building on the lead in? 
Floor control valves aren't explicitly defined but appear meet all the 
requirements of a "system riser" which is defined, and is the term used in the 
actual code material.

 
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.586.8111
www.bmwc.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120209/955cf7e9/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to