Thanks Mark,
I have a NFPA 13 system with a hydraulic elevator and a machine room in
the basement with a combustible shaft top so in WI we would need to put
one at the top / bottom in the machine room but NO control valves.
If the pipe is exposed at about 7'6" AFF would a box still be required?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mark
Jason
Sent: Wednesday, February 22, 2012 3:09 PM
To: [email protected]
Subject: RE: Elevators - Michigan rules

Yes, a monitored control valve is required in Michigan.  Location of
valve and box is also important.  Usually if you stand 6'-0" in front of
elevator door and rotate or spin 360 degrees you should be able to
locate it.  If its location is not visible from there they must have
signage pointing you in the right direction.  Of course, it's all on
what the AHJ will approve for location.  
I haven't put a head at the top of the shaft in years but you will need
one in the pit and machine room.  In some places you can eliminate the
head in the pit if it is an electric elevator in a non-com shaft with no
hydraulics.

Hope this helps,

Mark

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Wednesday, February 22, 2012 3:42 PM
To: SprinklerFORUM
Subject: Elevators - Michigan rules

I am designing a job in Michigan that will require sprinklers at the top
/ bottom of the elevator shaft and the equipment room.

Do these need to be provided with a shutoff valve/s?  

Thanks,

 

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120222/9ef83497/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to