We have just gone through this with jobs in Frisco and Lubbock, Texas, as
well as Colorado Springs. Tyco Thermal Controls has XL-Trace which is
listed (under certain guidelines) for fire protection piping.
The approvals through CSA include both steel and CPVC, and can be used on
branchlines with sprinklers. Not so clear under the UL guidelines. Right
now, the City of Frisco is reviewing the data to determine the proper
applications, per both listings.
As far as supervision goes, we have the alarm company connect to the panel
to give a trouble signal in the event of malfunction, i.e. loss of power,
etc.
----- Original Message -----
From: "Randy Knutson" <[email protected]>
To: <[email protected]>
Sent: Tuesday, February 28, 2012 10:37 AM
Subject: Heat Trace Supervision
8.16.4.1.4 "Where listed heat tracing systems are used, they shall be
supervised."
What are the minimum requirements for supervision?(such as; ground fault,
loss of power, .)
We have a 20' section of 4" bulk main that crosses an unheated corridor
What are the options out there for listed heat trace manufacturers for
freeze protection of bulk mains?
Thanks,
Randy Knutson, CET
Sales Manager
Shilo Automatic Sprinkler, Inc.
=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 9.0.0.909, Virus/Spyware Database: 6.19350)
http://www.pctools.com/
=======
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120228/b316cfbd/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum