The only thing confusing is if it's OH2 without a ceiling and then a ceiling is 
added later making it a combustible concealed space.


Ron Fletcher
Aero Automatic
Phoenix, AZ




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Vince Sabolik
Sent: Monday, March 12, 2012 3:01 PM
To: [email protected]; [email protected]
Subject: RE: SLOPAGE STUFF

THANK YOU ALL

So, what we have is this??????:

1.      There's no such thing as a .10 density 
under a roof that's pitched at or more than 4:12

2.      Spacing can be as much as 15 ft on the 
slope, but if it exceeds 8 ft on the flat,
         a minimum head pressure of 20 psi must be used.

3.      In no case can spacing on the flat exceed 10 ft.

Seriously, does anyone else find the table in NFPA confusing?


At 03:19 PM 3/12/2012, you wrote:
>Vince,
>In regard to slopeage stuff, I believe that what is being said is that 
>the you figure pipe length based on slopeage of pipe, but you figure 
>coverage area based on the flat.  Hope that helps.
>
>Bob Knight, CET III
>208-318-3057
>www.firebyknight.com
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Vince 
>Sabolik
>Sent: Monday, March 12, 2012 1:11 PM
>To: [email protected]
>Subject: SLOPAGE STUFF
>
>Need some help w/ dry sprinkler spacing before I hang myself along with 
>the pipe!
>
>Referring to Table 8.6.2.2.1 (a) - (spacing along slopes),
>
>I have this condition:
>
>Wood trusses, 36 in or less, pitching 6"/ft
>
>The "bay" is 31-0 actual, resulting in a line spacing of  10-4, or 
>11-6½ on that slope.
>
>My question:
>
>Does that slope dimension of 11-6½  - apply to the perpendicular 
>dimension of 10 ft in that table?
>
>If not, can someone make sense of this?
>
>
>Vince Sabolik, West Tech Fire Protection, Inc.
>11351 Pearl Road / Strongsville, Ohio
>44136       440 238-4800     Fax 440 238-4876
>____________________________________________________________________
>
>
>-------------- next part -------------- An HTML attachment was 
>scrubbed...
>URL:
><http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
>hment
>s/20120312/7d2a02f6/attachment.html>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>-----
>No virus found in this message.
>Checked by AVG - www.avg.com
>Version: 2012.0.1913 / Virus Database: 2114/4866 - Release Date: 
>03/12/12
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>__________ Information from ESET NOD32 Antivirus, version of virus 
>signature database 6961 (20120312) __________
>
>The message was checked by ESET NOD32 Antivirus.
>
>http://www.eset.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120312/5690dca4/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to