In the "old days" heads were staggered to help even out the flow as well as 
hasten the acttivation. 



David Bohannon 



Fire Sprinkler Plan Review City of Atlanta 



Department of Planning and Community Development 



Office of Buildings 



55 Trinity Avenue 



Suite 3900 



Atlanta, GA 30303 



e-mail: dbohan...@atlantaga.gov 



phone:  404-330-6193 



fax:  404-739-4172 







----- Original Message -----


From: "Mark Sornsin" <mark.sorn...@ulteig.com> 
To: sprinklerforum@firesprinkler.org 
Sent: Wednesday, April 25, 2012 4:18:18 PM 
Subject: RE: Rounding off {Squaring off?} 

I think it ultimately goes to the fact that they needed a simple way to space 
sprinklers and square is much easier to work with than round. 

As to the safety factor, Bruce pretty much hit it: it works. What is implied is 
that whatever the safety factor is it must be enough. The problem is, if you 
try to analyze the actual factor of safety you have to first ignore several 
other potential influences on that factor. Accuracy of the water supply 
information; actual pressure at the sprinkler; choice in design area (which may 
be affecting the actual pressure on the sprinklers); effect on calculations of 
including hose allowances and/or domestic allowances; effect on calculations of 
using assumed (vs actual) friction coefficients for the pipes; etc. When some 
people make the point that sprinkler calculations have 'so much' safety factor 
built into them they are essentially correct. But why do people make those 
assertions? Usually it is to justify lack of conformity to standards; and the 
problem with going down that road is that none of these above influences can be 
precisely measured in terms of additional safety factor they may or may not be 
providing. True, some jurisdictions will waive hose allowances in calculations 
under limited circumstances if it means saving the added cost of a pump and/or 
tank. Certainly the knowledge of the remaining potential factors of safety is a 
reason for doing this (on a limited basis). But you don't want to push it any 
farther than disregarding one fairly measurable variable because uncertainty 
raises exponentially with each added variable. 

So the bottom line in my view is that one could certainly do a mathematical 
exercise where they calculate the safety factor of all of the overlap in 
sprinkler sprays; but first they would have to make assumptions about those 
other influences. By the time they are done doing that, the exercise is nearly 
worthless, except as a bit of intrigue for those of us in the business. 

BTW - you can go to some manufacturer's web sites and view sprinkler spray 
patters. If you look at the Viking M 1/2 in. upright, you'll see that at 7psi, 
the spray from about 8 ft. above the floor reaches just over 9 ft. from the 
centerline of the sprinkler. In a Light Hazard Occupancy, that overlaps the 
7'-6" maximum distance, but does not reach the maximum diagonal distance of 
10.6 ft.  At 30 psi, you get closer to the 10.6 ft. Obviously, at smaller 
spacing, the overlap increases (another variable to consider). 

Mark A. Sornsin, PE| Fire Protection Engineer 
Ulteig Engineers, Inc.| Fargo, ND  
mark.sorn...@ulteig.com 


-----Original Message----- 
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bruce Verhei 
Sent: Tuesday, April 24, 2012 12:51 PM 
To: sprinklerforum@firesprinkler.org 
Subject: Re: Rounding off {Squaring off?} 

I've read in the past that this fell in the not well understood effect category 
when engineers have desired to model how sprinklers actually work. This seems 
to be difficult.  They say something that ends with but sprinklers installed 
and maintained to standards have a remarkable record of controlling fires in 
buildings. 

I want to buy one of the square heads.  Are the threads square too? 

Bruce 

Sent from my Motorola ATRIX™ 4G on AT&T 

-----Original message----- 
From: Thomas Watt <firesprinklerssaveli...@gmail.com> 
To: sprinklerforum@firesprinkler.org 
Sent: Tue, Apr 24, 2012 13:05:01 GMT+00:00 
Subject: Rounding off {Squaring off?} 

I had a brain-fart and came up with this question for the forum. Especially the 
engineers.  Since sprinklers, in general, throw in a circular pattern, and we 
calc the sprinklers as squares, there is always overlap so we are by default 
miscalculating a percentage of the density. Has anyone ever calculated the 
safety factor effect by ignoring the arcs outside the square??? 

Thomas 
A+ fitter/Foreman 
No work in Orlando, FL area 
Willing to relocate 
-------------- next part -------------- 
An HTML attachment was scrubbed... 
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120424/5639c5b1/attachment.html>
 
_______________________________________________ 
Sprinklerforum mailing list 
Sprinklerforum@firesprinkler.org 
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
-------------- next part -------------- 
An HTML attachment was scrubbed... 
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120424/50c0be9e/attachment.html>
 
_______________________________________________ 
Sprinklerforum mailing list 
Sprinklerforum@firesprinkler.org 
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
_______________________________________________ 
Sprinklerforum mailing list 
Sprinklerforum@firesprinkler.org 
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120426/f2dde620/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to