What George said..
As far as short cycling, I've found a walk-around for D systems, maybe
usable for R.  I put an off-delay on the contactor and set for 1-10 minutes.
I've done a few 13D tank and pump systems lately and been using a nice panel
made by C-H which has this.  In fact, I just wired one with a programmable
timeclock for weekly runs with the off-delay.  You have to be careful with
drawing from tanks alongside the pump and relatively zero npsh and use a
large enough suction pipe to flood the pump or you will pull a slight vacuum
and derate the pump.  I haven't measured exact flow vs. pressure of these
little D pumps as the inspectors test is piped back into the tank(s) but it
looks marginal (using good gauges)  in making it's 'published' curve.  
TD