To specifically answer this questions, yes, Chapter 7 Hydraulically Designed Sprinkler Systems, 1976 edition with light hazard and the three ordinary hazard curve sin Chapter 2.
Scott Futrell (763) 425-1001 x 12 Office (612) 759-5556 Cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Tom Duross Sent: Monday, May 07, 2012 6:39 PM To: [email protected] Subject: 1976 13 Question Would anyone with a library know if hydraulics were referenced in the 1976 edition of NFPA 13? I'm going to be replacing a dry system with MIC installed in 1984 under this edition. It almost looks pipe scheduled except for the main (assuming the schedules for LH haven't changed). I'm assuming the 30% increase wasn't there either. :P Analyzing the existing system hydraulically, I have densities in excess of 0.5 in the larger areas with not more than 80-90 SF per head throughout. TD _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum