FM loosens transverse flue requirements with in-racks, is this also the intention of 2010 NFPA 13. Transverse flue spaces remain very important to ceiling-only sprinkler protection.
16.2.4.2.3.2 ...if no transverse flues, then in-racks not to exceed maximum spacing 16.1.10.2. transverse flues are nominally 150-mm (6 inch). Because 16.2.4.2.3.2 is the more specific prescription, may we assume its precedence? Scot Deal Excelsior Fire gsm: +61 (0)435 292 599 -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120529/2bd1e4cc/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum