FM loosens transverse flue requirements with in-racks,
is this also the intention of 2010 NFPA 13.  Transverse
flue spaces remain very important to ceiling-only sprinkler protection.

16.2.4.2.3.2  ...if no transverse flues, then in-racks not to exceed
maximum spacing

16.1.10.2.  transverse flues are nominally 150-mm (6 inch).

Because 16.2.4.2.3.2 is the more specific prescription, may we
assume its precedence?


Scot Deal
Excelsior Fire
gsm:  +61 (0)435 292 599