Why not cut a 100mm (4") slot across the centre of each 2.3m(7'-6") shelf
thus producing a transverse flue and reducing the shelf size to that of a
pallet and it becomes open shelves. If product could encroach on flue space
fit edge barriers or mesh to ensure flue is kept clear. 

Russell Gregory
Ph  03 338 4853
e-mail [email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of J.P. Merlino/
Ing.L.Lagomarsino y Asoc.
Sent: Saturday, 9 June 2012 8:50 AM
To: [email protected]
Subject: Shelf storage for pharmaceuticals

Gentlemen:

We are dealing with a warehouse for pharmaceutical commodities (class IV),
where  we have racks and also 5 rows of solid shelf structure 20 ft high
with solid shelves spaced vertically 14 inches. 

Shelf dimensions are 7,5 ft x 3 ft. ( 23 sq ft), arranged so that the
lateral flue space is of 5 inches.

Roof height is 40 ft.

The question regards protection criteria for the solid shelf structures.

Per NFPA 13 definition, our shelves do not comply with the maximum depth of
30 inches. Our shelves have 36 inches.  Also there are not provisions for
shelf storage with a height above 15 ft.

Commentary to 14.2.1 on the handbook ( 2010 Edition, page 562) says that
shelf storage exceeding 15 ft. can be protected according criteria for rack
storage in chapter 16.

The issue is that it does not seems possible or effective  to protect this
solid shelve structure with in-rack sprinklers. 

It appears that there is no criteria to protect this with only ceiling
sprinklers. CMSA and ESFR does not apply to shelf storage.

Any idea on how to solve this? 

J.P. Merlino
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120608/797aea76/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to