I satisfied my goofy curiosity "which will activate first, a 155F Standard
Response or a 200F Quick Response"?  And the winner is... BOTH !, depending
on Ceiling Height. At C.H.= 13'-1 1/2" the 200F QR blew at 24.0 sec. The
155F SR at 26.3 sec. At C.H.= 19'-8" the 155F SR popped at 29.2 sec. The
200F QR at 30.9 sec. The reason is, RTI is established using empirical
measurements of the temperature and velocity of the air-- the temp falls
like a rock with greater horizontal dist from the fire, where-as the
velocity varies with ceiling height.

I was going to title this thread "well i'll be a monkey's uncle" for having
bad-mouthed NFPA #13 regarding the QR Reduction at 20 Feet Glitch Q__o.

For both scenarios I used a 2 megawatt fire, and the heads were 6'-7" from
the center of the plume, with a floor and ceiling only (no walls).

 