Ah! Thanks Jeff, that's pretty much what I was looking for and is good in this 
case where the PRV is close to the fire pump!
Thanks,


--- On Wed, 6/20/12, Jeff Garrison <jeffgarrison1...@gmail.com> wrote:

From: Jeff Garrison <jeffgarrison1...@gmail.com>
Subject: Re: Calculating Pressure Reducing Valves
To: sprinklerforum@firesprinkler.org
Date: Wednesday, June 20, 2012, 10:55 AM

In HydraCalc you can give a fixed PSI "limiter" to a fire pump, it will
flat-line the curve above that PSI.

On Tue, Jun 19, 2012 at 5:54 PM, Vince Sabolik <vi...@wtfp.net> wrote:

> I've done this a couple of times before - for GSA, no less.
>
> Believe it or not, part of that dramatic pressure drop across that valve
> IS friction loss.
> The manuacturer will usually give you a loss table. In my case I showed
> that loss (friction) in the appropriate
> column and let the less be a fixed drop.
>
> Hope this makes sense
>
> At 05:03 PM 6/19/2012, you wrote:
>
>> I have an existing install that needs to be re-calculated due to some
>> modifications. The system has a booster pump and downstream of the
>> discharge, before the feed main disappears into the structure, there is a
>> pressure reducing valve which is sett to 150 psi. I would like some
>> confirmation that I'm calculating this thing right (hydracalc).
>> I've set up a couple of nodes for the PRV and for the first run I set the
>> friction loss at 0 to get an idea of what the discharge pressure is at the
>> point of the PRV. Then I basically go back and enter in the difference of
>> the pump net pressure and the PRV setting of 150 psi as the fixed friction
>> loss through the PRV's nodes. So for example, let's say the pump is capable
>> of 200 psi at my system demand and the PRV is at 150 psi - I set the fixed
>> friction loss at the PRV to 50 psi to achieve the pressure reduction. Does
>> this sound about right?
>>
>> This is more of a software question than anything I suppose but any input
>> is appreciated.
>> Thanks!
>> RB
>> -------------- next part --------------
>> An HTML attachment was scrubbed...
>> URL: <http://fireball.**firesprinkler.org/mailman/**
>> private/sprinklerforum/**attachments/20120619/158d91e4/**attachment.html<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120619/158d91e4/attachment.html>
>> >
>> ______________________________**_________________
>> Sprinklerforum mailing list
>> Sprinklerforum@firesprinkler.**org <Sprinklerforum@firesprinkler.org>
>> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>>
>> __________ Information from ESET NOD32 Antivirus, version of virus
>> signature database 7233 (20120619) __________
>>
>> The message was checked by ESET NOD32 Antivirus.
>>
>
>
> Vince Sabolik, West Tech Fire Protection, Inc.
> 11351 Pearl Road / Strongsville, Ohio 44136       440 238-4800     Fax 440
> 238-4876
> ______________________________**______________________________**________
>  -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://fireball.**firesprinkler.org/mailman/**
> private/sprinklerforum/**attachments/20120619/3fd6cb22/**attachment.html<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120619/3fd6cb22/attachment.html>
> >
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.**org <Sprinklerforum@firesprinkler.org>
> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120620/ba9609f2/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120620/d894b449/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to