I have a situation which seems to be occurring frequently now. In unfinished 
basements, wood joist construction, I have a large amount of ductwork. The 
ducts are causing numerous obstructions. It seems a little unrealistic to be 
placing residential pendents in every little pocket which is "obstructed" if 
following the letter of the code. During the survey, it occurred to me & 
another workmate that if approached from a performance based standpoint, a good 
option would be to use quick response uprights with reasonable head spacing. I 
understand that this is not really addressed in 13-D. I feel however that the 
whole ("positioned in a manner that anticipates future installation of a 
finished ceiling" is a somewhat optimistic & unrealistic  approach & left open 
to pretty wide interpretations. Some additional factors that went into my think:
.Some of the ducts hang down from the ceiling & allow spray to go over the top
.At this unfinished stage, the only walls are the foundation walls & this is 
not a living space so wall wetting probably isn't a big issue
. I have enough water to drive the 2 uprights at a .10 density up to about 250 
sq. ft. each
. The system would lend itself well to future alterations 

I realize I may have a battle on my hand trying to get this thru the AHJ, but, 
I would like to hear opinions on this topic and/or other ideas.
Thanks for your help.

Regards,
  
Michael G. Haley
[email protected] 