Do floor to ceiling curtains in an office with 10 ft.  ceiling change the 
office to OH?

Ron Fletcher
Aero Automatic
Phoenix, AZ




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, July 25, 2012 3:55 PM
To: [email protected]
Subject: Re: Stage/platform

Get rid of the curtain... LH.  Done
John Drucker - Mobile Email

----- Original Message -----
From: [email protected] 
<[email protected]>
To: [email protected] <[email protected]>
Sent: Wed Jul 25 18:39:08 2012
Subject: RE: Stage/platform

Agree with you up to the end.  It's a Multi-Purpose building with a platform 
that has a low ceiling and a horizontally closing curtain.  Not a performing 
arts center or other "legitimate" stage type of facility.
So the building is used for PTA meetings, student assemblies and cafeteria 
seating; it's a smaller A-group with a raised platform that faces the main 
seating area, and I see the whole thing as light hazard.


The plans reviewer brought this up at the very end of a backcheck.  The entire 
design is approved, and this wasn't a correction on the first plan check. She 
brought it up right before we were to get signed off and it's a big deal 
because the riser is at the other end of the building.
So this will change our piping plan and RCP over the platform, main size, 
seismic bracing calc's, detail sheet, etc., etc.  That's why it's a BFD ...

SML




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, July 25, 2012 3:32 PM
To: [email protected]
Subject: RE: Stage/platform


For example.......... An A-1 Theatre, IIA Construction, 1 story, 10,000 sf in 
area, exit discharge at grade, occupant load of 299.  Does the building need 
sprinklers ? 

903.2.1.1 Group A-1.

An automatic sprinkler system shall be provided for Group A-1 occupancies where 
ONE of the following conditions exists: 
1.      The fire area exceeds 12,000 square feet (1115 m2).
2.      The fire area has an occupant load of 300 or more.
3.      The fire area is located on a floor other than the level of exit
discharge.
4.      The fire area contains a multitheater complex.

Lets add a Stage........

401.1 Detailed use and occupancy requirements.

In ADDITION to the occupancy and construction requirements in this code, the 
provisions of this chapter apply to the special uses and occupancies described 
herein.

[F] 410.6 Automatic sprinkler system.
Stages shall be equipped with an automatic fire-extinguishing system in 
accordance with Chapter 9. Sprinklers shall be installed under the roof and 
gridiron and under all catwalks and galleries over the stage.
Sprinklers shall be installed in dressing rooms, performer lounges, shops and 
storerooms accessory to such stages.

Exceptions:
1.      Sprinklers are not required under stage areas less than 4 feet
(1219
mm) in clear height that are utilized exclusively for storage of tables and 
chairs, provided the concealed space is separated from the adjacent spaces by 
not less than 5/8-inch (15.9 mm) Type X gypsum board.
2.      Sprinklers are not required for stages 1,000 square feet (93 m2)
or
less in area and 50 feet (15 240 mm) or less in height where curtains, scenery 
or other combustible hangings are not retractable vertically.
Combustible hangings shall be limited to a single main curtain, borders, legs 
and a single backdrop.
3.      Sprinklers are not required within portable orchestra enclosures
on
stages.

So 410.6 could require the suppression of a stage in an otherwise unsprinklered 
building.  Of course I really oversimplified this, obviously means of egress 
figures into the equation.

If your building requires sprinklers based in 903, 410.6 is a mute point since 
sprinklers are required throughout and the density based on the hazard from 13, 
OH-2.

John


John Drucker, CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or otherwise.  
Obtain required applications, permits, inspections and approvals from 
Authority(s) Having Jurisdiction. 



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Wednesday, July 25, 2012 6:16 PM
To: [email protected]
Subject: RE: Stage/platform

But 410.6 excepts sprinklers where stages are less than 1,000 s.f. in area and 
50' high AND where there is only a "main curtain".  This is the fulcrum of the 
widget: they're saying that the curtain that closes in front of the
stage is an "overhead  hanging curtain".   This thing has a t-bar
ceiling at
9'-0 or 10'-0.

We're putting in sprinklers either way as it's a fully sprinklered building but 
absent a volume of "flag and bag" space above the stage,
OH-2 is a BFD and in my opinion not required on this particular application.


Steve 




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, July 25, 2012 3:10 PM
To: [email protected]
Subject: RE: Stage/platform

2006 IBC Commentary......................

Platform

"Platforms are raised areas that are used for public performances and 
presentations that EXCEPT FOR LIGHTING DO NOT INCORPORATE ANY OVERHEAD HANGING 
CURTAINS, DROPS, SCENERY OR STAGE EFFECTS."

 
OVERHEAD HANGING CURTAINS..... It's a stage.  

Sprinklers.... 410.6
Standpipes (You're favorite) .... 410.7

Hope that helps,

John Drucker, CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or otherwise.  
Obtain required applications, permits, inspections and approvals from 
Authority(s) Having Jurisdiction. 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Wednesday, July 25, 2012 1:59 PM
To: [email protected]
Subject: Stage/platform

Friends, Romans, Forumite and Drucker:

I have a plans reviewer with whom we are dancing about on the subject of 
defining a "platform" vs. a "stage".  Probably the largest part of the 
conversation has to do with "overhead hanging curtains".  The definition of a 
stage is basically a space within a building used for entertainment or 
presentations that includes "overhead hanging curtains, drops,
scenery or stage effects other than lighting and sound."   

My take is that this space in an elementary school MP buildings is a platform 
because it only has lighting and sound overhead.  Their take is that it's a 
stage because it has a curtain that can be drawn across its
front.   Anyone have a more specific definition or code citation for
what constitutes an overhead hanging curtain?

Steve Leyton



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120725/9e59c125/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to