Really depends on how extensive it is.  You may be able to treat it with
localized protection per 13 8.15.1.5 (2010).

Bob Knight, CET III
208-318-3057
www.firebyknight.com




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, July 26, 2012 2:27 PM
To: [email protected]
Subject: non combustible concealed space?

Well known restaurant chain is inquiring about this situation:

If you have a non-combustible structure with new wood framed walls within,
there will be 2x4 bracing from the top of said wood walls attached to the
bar joists. Does the tops of the walls and the bracing alone make this a
combustible concealed space that requires protection? I have never seen it
so, but evidently they are receiving info that it does.

Thanks,
Greg

--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>