NFPA #13 says that the maximum deflector distance for EC heads (non-comb, unobstructed const) is 12". All of the EC Pensents I am looking at only have Flat Esc. or Semi-rec plates listed.
Can you use 401 style plates with these heads even thought they are not specifically listed? My thoughts are that you can because if you used bare pipe you place the head 12" below the ceiling, so if that is true and you choose to cover the pipe with Deep Plates, it should not be a problem. Thanks, -- Greg McGahan Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120731/27a6be42/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum