Greg,

Jim touched on many of the issues here that go WAAAAAAY beyond the 
responsibility of a sprinkler contractor.  I'm not trying to diminish anyone's 
credibility or ability but there are a lot of issues which need to be addressed 
by several parties to be sure this building is code compliant before you even 
turn the first pipe wrench.  

I'm not sure either where the 12,000 sq. ft is coming from other than for an 
S-1 storage occupancy you have to have sprinklers if you exceed that sq. ft. 
per the IBC.   Maybe he have meant Cubic Ft since with 4 control areas that's 
the most he could get and not be forced into the H-3 occupancy.   And the "high 
hazard" sprinkler system?  What's that?   If you apply NFPA 55, it's only 
looking for OH2 at 3,000 sf as base line.    

Either way the tenant isn't getting 20,000 cf in the warehouse without it going 
to an H-3 which then drives a whole bunch of other requirements for other 
disciplines that can get quite pricey.   

Storage occupancies are always a lot of fun, but it becomes more difficult when 
the areas have been assigned the wrong occupancy or the architect has not 
considered the actual materials used and stored within.  Then again, the owner 
may have "forgotten" to tell the architect what was going in there during the 
design phase.  

No matter what, this all needs to be thrown back to the architect to be sure 
the area's occupancies are properly defined based on code definitions and use.  
  


Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jim Davidson
Sent: Friday, August 10, 2012 3:06 PM
To: [email protected]
Subject: RE: 02 storage

What is the occupancy that is moving into the building? Per the IBC
Table 307.1(1) you are permitted to have 3,000 cubic ft of oxidizing gas
in a facility any amount greater than this amount will change the use
group to an H-3 Hazardous Use Group. NFPA 55 does not reference any of
the building code required fire separation ratings between different use
groups. Other issues will be how will the cylinders be filled? Will
there be cryogenic oxygen stored? Will there be trans-filling of
containers? What type of floor surface is in the area. If a hydrocarbon
based product oxygen-enriched atmosphere can cause these products to
ignite faster, and burn faster and hotter than usual. NFPA 55 only
requires a one hour separation while the IBC requires up to a 2 hour
fire separation between occupancies. 

Someone needs to sit down with the owner and explain that this issue is
not in the realm of the sprinkler contractor's expertise unless the
contractor would like to add to their uninsured liability potential.

This would require an engineering analysis by a FPE who has experience
in industrial gas storage facilities and Hazardous Use Group Occupancies
of the IBC. If you think Mechanical PE's practicing in the discipline of
fire protection are funny, wait until you see them perform in the
industrial gas arena.           

Have a fire safe day!

Regards

Jim

DAVIDSON ASSOCIATES

Fire Protection Engineering     P. O. Box 4010
Code Consultants        Greenville, DE  19807-0010
Medical Gas Systems Engineering (302) 994-9500
        Fax (302) 234-1781

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg
McGahan
Sent: Friday, August 10, 2012 2:01 PM
To: [email protected]
Subject: 02 storage

This is a completely new area for me so any help is appreciated.

Issue:  Medical Gas Storage of 02 only in various cylinders.

The tenant and owner of this Commercial / Industrial Strip center is
having difficulty with the AHJ who claims that even if they classify the
warehouse portion of this space as Storage Occupancy instead of
Business, The maximum cubic footage of 02 allowed to be stored in one
place is 12,000 with "High Hazard" Sprinkler protection. The tenant
needs to store almost 20,000 cubic feet.

Does anyone have expertise in this area?
Thanks,
Greg


--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120810/f3e9c5a0/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to