George,

If I'm understanding the question my read is that you're supposed to cover
under the first landing because of the likelihood of debris gathering there
and/or the likelihood of that becoming a storage area. Stairs and landings
are considered clear of or with very little debris and protected from the
ceiling of the stairwell.

On Mon, Aug 20, 2012 at 6:18 PM, George Medina Jr <[email protected]> wrote:

>
>  Ok, I need a little clarification on another obviously simple question
> again (mental block).
>
> NFPA-13, 2010 Ed. Section 8.15.3.2.1
> Does the reference to 'the first accessible landing' include the portion
> of the stairs from the ground to the mid landing and between the mid
> landing and the 2nd floor?
>
>
>
>
>
> George Medina Jr.
> Sr. Fire Sprinkler Designer
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120820/1123e4d8/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120820/6fef65df/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to