The only reference to 101 is within 13, very first page pushing to
Chapter 2 and Annex F.   Where Chapter 2 doesn't reference it, but Annex
F does.

And like everyone else, we have multiple jurisdictions to deal with,
none of which will be definitive and will burden the PE with the
liability.


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Wednesday, September 26, 2012 4:35 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Stupid closet question...

Does your state or jurisdiction formally adopt 101? (Most don't.).  If
101 is equal to or supersedes the building code, you may be able to take
it, but remember that it's Annex material. Most AHJ's see it as "code
says to sprinkler per 13, 13 says to sprinkler it, so sprinkler it."

Steve

C&H Fire - Mike Gallello <mgalle...@chfireinc.com> wrote:

It's likely been asked before, but I don't recall - so please excuse my
possible ignorance!

NFPA 13, 2010 - 8.15.8.2 Dwelling units, closets - hotels and motels
they can be deleted, conditionally regarding the 24sf and 3ft rule.

Annex D (Pulled from NFPA 101) in two separate areas (D1.1.6.1 &
D2.19.2.1) states that closets under 12sf in dwelling units shall not be
required to be sprinklered.  The referenced 101 code is stated there as
well...

I'm looking at it that the paragraphs of 101 referencing closets under
12sf in dwelling units permits the omitting of sprinklers within these
closets.  (Not any with equipment of course).  There are some others
here that disagree, stating that since 13 addresses it, 101 isn't
applicable and that heads are required in the closets period.

Anyone else have this kind of throw down in your offices?
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to