2010 ed. of the standard, 17.3.1.1 sez that Group A in cartons (presuming this includes expanded and unexpanded) shall be protected per Table 17.3.1.1 and with in-rack sprinklers per the Figures 17.3.1.2(a) or (b). Then you read on to 17.3.4.1.4, which is singe-row and double-row in-rack sprinkler criteria, and it gives you a direct prescriptive per Figure 17.3.4.1.4 (albeit with only the higher roof density of the two to choose from in Table 17.3.1.1), which appears to be a way simpler in-rack arrangement, without face sprinklers. What am I not understanding and which one precedes (or supersedes) the other?
Steve Leyton PROTECTION DESIGN & CONSULTING 2851 Camino del Rio South, Suite 400 San Diego, CA 92108 ------------------------------------------------------------- Ph: 858.751.2930 - ext. 102 Fax: 858.751.2933 Cell: 619.972.5696 -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121021/0e285ef7/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum