Be careful, the joint commission is still on the 2000 edition of NFPA 101, 
momentarily.

Duane Johnson
________________________________________
From: Johnson, Duane (NIH/OD/ORS) [C]
Sent: Tuesday, October 30, 2012 1:38 PM
To: [email protected]
Subject: RE: Hospital - Closets vs Lockers

NFPA 101 (12 ed):19.3.5.10    Sprinklers shall not be required in clothes 
closets of patient sleeping rooms in hospitals where the area of the closet 
does not exceed 6 ft2 (0.55 m2), provided that the distance from the sprinkler 
in the patient sleeping room to the back wall of the closet does not exceed the 
maximum distance permitted by NFPA 13, Standard for the Installation of 
Sprinkler Systems.

A.19.3.5.10 Although this exception is currently not recognized by NFPA 13, 
Standard for the Installation of Sprinkler Systems, a proposal for such 
exemption has been submitted for consideration by the Technical Committee on 
Sprinkler System Installation Criteria. This exception is limited to hospitals, 
as nursing homes and many limited care facilities might have more combustibles 
within the closets. The limited amount of clothing found in the small clothes 
closets in hospital patient rooms is typically far less than the amount of 
combustibles in casework cabinets that do not require sprinkler protection, 
such as nurse servers. In many hospitals, especially new hospitals, it is 
difficult to make a distinction between clothes closets and cabinet work. The 
exception is far more restrictive than similar exceptions for hotels and 
apartment buildings. NFPA 13 already permits the omission of sprinklers in 
wardrobes [see 8.1.1(7) of NFPA 13]. It is not the intent of 19.3.5.10 to aff
 ect the wardrobe provisions of NFPA 13. It is the intent that the sprinkler 
protection in the room covers the closet as if there were no door on the 
closet. (See 8.5.3.2.3 of NFPA 13.)


Duane Johnson
________________________________________

From: C&H Fire - Mike Gallello [[email protected]]
Sent: Tuesday, October 30, 2012 10:59 AM
To: [email protected]
Subject: Hospital - Closets vs Lockers

Ok, stupid question of the day - Existing hospital, patient recovery
rooms - there are existing "closets" that are going to be incredibly
difficult to install fire sprinklers in.

However, I'm not sure if these need to be protected at all.

When is a closet not a closet, but a 'locker'?

They are framed walls, lathe and plaster with a hard lid.  6'0 from the
floor to the hard lid, 12x16 inch footprint.  At the 5'-0 level is a
shelf, at the 4'0 level is a clothes hanger rod.  The closet floor is
not at the level of the patient room floor, elevated appx 6" with a kick
plate.   The door does not have openings at the top or bottom, can be
considered "full height" and does separate the floor area of the patient
room from the "floor" of these closets, the door is solid, not
self-closing and not rated.

I'm not sure what other details would be pertinent, however feel free to
ask.

At the risk sounding pushy, time is a factor with this "challenge".

Thanks,
Mike Gallello
C&H Fire

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to