This is poorly worded for one thing.

Typically the mandate of reduction of flow to fire sprinkler systems when the 
municipal supply pressure falls to or below 20 psi is a requirement of the 
local water purveyor.  This doesn't always result in the water supply being 
completely shut off, it can be throttled back so that the source pressure is 
maintained to the minimum set point.  However this does have an effect on 
sprinkler discharge and hose discharge.

To accomplish this you install a low suction control valve in the main system 
supply.  

If you have a high value or high risk installation and the local water purveyor 
has this requirement, it's a good idea to let the owner know this puts their 
property at risk and to consider an on-site water storage tank and pump, 
especially if the local water supply is weak to marginal.  

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Timothy W Goins
Sent: Monday, November 12, 2012 12:20 PM
To: [email protected]
Subject: 20 PSI Minimum

How are others addressing the 20 PSI minimum operating pressures of the fire 
sprinkler system? Here is a quote from a spec that I have received.

"The fire protection systems shall not be designed to operate if the residual

pressure of the existing water service falls to 20 psi or lower at design flow

requirements."

 

Timothy W Goins
A & T Services

 

"For I am not ashamed of the gospel of Christ: for it is the power of God unto 
salvation to everyone that believeth;." KJV Romans 1:16

 

Reply to   <mailto:[email protected]> mailto:[email protected]

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121112/9c2eef0f/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to