From: Sean Lockyer 
Sent: Wednesday, January 09, 2013 5:17 PM
To: '[email protected]'
Subject: Re: Pre-.05 density heads: What heads can be used as a replacement ?

 

Thanks Art and Mike-I have done so but they are just as lost as I. It seems the 
only solution is to do a complete re-calc of the existing system. The problem 
is that in those days, especially here in Florida, the sizes used are not the 
sizes you see today. Back then, all of the lines were ¾" and the mains were 
either 1" or 1-1/4". Sadly, not most foresight was given to what to do when 
these heads had to be replaced.

 

Globe is the only manufacturer that still produces replacement residential 
sprinklers. Reliable, Viking, Tyco, etc... all phased them out back in 
2004/2005. In addition, none of the manufacturers are willing to put their 
"professional opinions" on paper which is understandable due to the liability 
it would entail so that is why I am relying so much on hopefully NFPA, NFSA, 
AFSA, etc... addressing this somehow.....

 

Most local AHJ's would just as soon require them to be calculated but most 
contractors will not release old installation plans (if they still have them) 
and many local AHJ's do not keep records going back that far....

 

              Sean Lockyer

              Project Designer                               4617 Parkbreeze 
Court

              Cell    386-279-1197                              Orlando, 
Florida 32808

              [email protected] <mailto:[email protected]>    
           Phone:      407-816-9101

              www.AITLifeSafety.com <http://www.aitlifesafety.com/>             
           Fax:         407-816-9104

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130109/bc0f1e41/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 8903 bytes
Desc: image001.jpg
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130109/bc0f1e41/attachment.jpg>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to