I have been watching the forum for a while, but this is my first post.  So,
here goes….

 

Our industrial customer would like to convert an existing, indoor spray
booth with an air-wash filtration system to a dry filtration system (air
filters only).  The booth area is about 750 ft².  Make-up air is supplied
from plenums in the ceiling.  Most of the floor is steel grating over a sump
where the air-wash water accumulates, and the exhaust air exits the spray
booth.  The sump leads outside the building, below the exterior wall, and
then opens up to the grade where the air-wash plenum is mounted on top.  The
material applied is a water-based primer (20%-40% solids), for aluminum
aircraft panels, that contains chrome.  Yes, it is nasty stuff.  And, it
covers the entire floor as a yellow powder.

 

The spray booth is already sprinklered.  But, to replace the air-wash
system, we plan on installing two-piece arresting filters under the existing
floor grating in two locations and blanking off the remaining area.  A new
HEPA filter plenum will be installed in place of the existing air-washer;
outside on top of the sump.  And, pre-filters will now be installed in the
spray booth ceiling plenum.

 

Anyone have experience, with a similar setup, they would be willing to
share?

 

I’m thinking the now dry sump (exhaust path) will need to be protected as an
Extra Hazard, Group 2 area.  And, some or all of the sprinklers will need to
be intermediate level/rack storage type due to being under open grating,
even though they have the arresting filters or blanking plates overhead.
And, I’m planning on requiring UL 900 listed air filters.

 

One thing I’m not sure of is whether the thin cellophane or paper bags for
covering the sprinklers (NFPA 33 9.4.1) are the way to go for protecting the
sprinklers against overspray.

 

Does anyone have any history with these? 

 

Thanks in advance,

 

~David Knifton, P.E., LEED AP

  Rawlings Mechanical Corp.

  Ph: (323) 875-2040

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130110/20896548/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to