It seems like this could be done in a similar fashion to a 200lb system 
acceptance test.

We have small water pumps that can get the system up to 200 on a gauge 
connection. Fill with water, then connect small pump to top off pressure. No 
need to get a large pumper out there.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matthew J. Willis
Sent: Friday, January 25, 2013 9:13 AM
To: [email protected]
Subject: RE: Dry Standpipe 5 year pressure test enquiry.

Possible, not practical. 200psi for 2hrs. The Fire Truck will only be needed
like 2 minutes for that...

R/
Matt

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of MOWLE
Kevin(K) - BRUCE POWER
Sent: Friday, January 25, 2013 10:01 AM
To: '[email protected]'
Subject: Dry Standpipe 5 year pressure test enquiry.

 
As per NFPA 25(2011)  6.3.2  there is a 5 year requirement for the
hydrostatic pressure test of dry standpipes. 

We are looking at the possibility of utilizing a Fire Truck (pumper) to
complete this test. 

Has anyone else done this? Opinions?

Thanks
Kevin Mowle
Bruce Power
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to