Chris,

Hangar fires, just by head:
- 30 June 1968 Hangar 10 at Amsterdam Airport
- 5 May 2006 Sabena Technics "hangar 40" at Brussels Airport.
With some googling you might even find more.
Or are we just living in a dangerous neighbourhood?

Met vriendelijke groet / Yours sincerely,

Frans Stoop
TOS architecture & fire protection
Netherlands <[email protected]>
Tel. +31-24-324 0112


At 10:15 31-1-2013 -0600, you wrote:
Forgot about that one. Navy and DLA yes, all others when the waters supply without the pump cannot do 25% of the design area.

The question surrounds why do the Code protect hangars so much differently than about everything else. Certainly a plane owner or insurance company might want to but where is the threat to the public or occupants that is so much greater which is where the codes should IMHO focus on. I'd also throw in the lack of known fires in hangars. The Air Force recently looked and couldn't find a single fire in the last 50 years as it was related to me.

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN


-----Original Message-----
From: [email protected] [mailto:[email protected]] On Behalf Of Matt Smith
Sent: Thursday, January 31, 2013 9:59 AM
To: [email protected]
Subject: RE: Two Pumps

I believe it's still required at military installations per the UFC where what's being protected and fed by the pump has been determined to be mission critical.

Matt Smith
The Protection Engineering Group, Inc.
Baltimore, MD


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cahill, Christopher
Sent: Thursday, January 31, 2013 10:22 AM
To: [email protected]
Subject: Two Pumps

Can anyone definitively say where redundant fire pumps are required besides hangars per 409? I'm thinking maybe hospitals and high-rises or just super high-rises? I don't do enough of those to be sure. I'm asking required by Code not debating whether they are just a good idea in some occupancies.

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]<mailto:[email protected]>
www.burnsmcd.com<http://www.burnsmcd.com/>

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered
in: MN